You can: log in, read the tech support FAQ, or request your lost password. This dumb message (and those ads) will appear on every screen until you register! Get rid of this crap by registering your own SA Forums Account and joining roughly 150,000 Goons, for the one-time price of $9.95! We charge money because it costs us money per month for bills, and since we don't believe in showing ads to our users, we try to make the money back through forum registrations.
 
  • Post
  • Reply
babyeatingpsychopath
Oct 28, 2000
Forum Veteran


MrYenko posted:

I've encountered multiple (mostly recent-construction) homes with GFCI-protected garage circuits that have gently caress-all for proper insulation, and trip constantly, even with really innocuous loads on them. My old townhouse garage circuit would trip (it had a dedicated breaker, a GFCI receptacle, and an outdoor receptacle in a weatherproof box by the front door, down-circuit of that,) with just the garage door opener plugged in and operating, because the electrician probably scraped the poo poo out of the cabling when he was pulling it, or some other problem. I was never able to figure it out, and just lived with it.

The 5mA current leakage standard is a little aggressive for a garage circuit, IMO, particularly if there's also an outdoor receptacle on the circuit.

Agreed; garages should have GFPE instead. Those can be set to whatever the AHJ says is reasonable. We were allowed to set sump pump circuits at 250mA, which is enough to kill you dead. The maximum is GFPE on industrial services, which can be set to trip at 1200A (for a 3000A breaker).

The problem is that 10mA is the let-go limit, and people with weak hearts and lungs can die with as little as 20mA. So what do you raise the level to? The difference between 5mA and 10-15mA probably isn't worth another exception/section in the code book, another type of breaker/outlet, and another thing to be tested for in a slightly different way. So everything gets GFCI or AFCI.

Adbot
ADBOT LOVES YOU

other people
Jun 27, 2004
Associate Christ
oven guy again. I took the a panel off of the back of the oven and I do not immediately see anything wrong.

https://imgur.com/a/TQxk9

My wife did point out this bit that looks like it is scorched?

https://imgur.com/a/dgrS2


Otherwise, it all looks pretty dull to me?

H110Hawk
Dec 28, 2006

other people posted:

My wife did point out this bit that looks like it is scorched?

https://imgur.com/a/dgrS2

That is scorched, which is incorrect. It should all be a uniform offwhiteish color. You need to lookup how to replace it, or let the appliance guy replace it. Sadly it's a rivet holding it in, hopefully that piece unclips.

other people
Jun 27, 2004
Associate Christ
:o so this piece is the socket for the oven light.

http://imgur.com/a/fopju


It was simple to remove and if I can find a replacement will be simple to put back in. Do you think it could explain the behaviour?

H110Hawk
Dec 28, 2006

other people posted:

:o so this piece is the socket for the oven light.

http://imgur.com/a/fopju


It was simple to remove and if I can find a replacement will be simple to put back in. Do you think it could explain the behaviour?

(I realize post shower) unless that discoloration is normal for a gas range. Might want to hit up google, but if those parts have sorta melted internally yes it could. It could also be entirely unrelated, or one of several problems. The joys of electricity. What is the make and model of your stove?

It doesn't answer why they look like that in the first place, unless the light bulb socket was root cause. Taking the parts to an appliance repair place and gauging the look on their face should tell you if it's correct or not.

other people
Jun 27, 2004
Associate Christ
It is a Frigidaire FGF337ECC. The part looks to be # PS439060 which I can have shipped here for $35. I am going to try this instead of the handy man and see what comes of it.

If it doesn't work then we can get a new oven :p.

kid sinister
Nov 16, 2002

other people posted:

It is a Frigidaire FGF337ECC. The part looks to be # PS439060 which I can have shipped here for $35. I am going to try this instead of the handy man and see what comes of it.

If it doesn't work then we can get a new oven :p.

$35 for a friggin light bulb socket??? What a rip-off.

Still, you have a hot to ground short, correct? Or was it hot to neutral?

Guy Axlerod
Dec 29, 2008
Try just disconnecting the scorched part. Do you still trip the breaker when you plug in the appliance?

other people
Jun 27, 2004
Associate Christ

Guy Axlerod posted:

Try just disconnecting the scorched part. Do you still trip the breaker when you plug in the appliance?

ohhhh. I could just tape over the end of the wires for the socket and put it back together?

i'll try this..


also, ebay had TWO sockets for less than the cost of one at other places but then i have to deal with weird ebay people and what would i do with two???



edit: it works! i taped over the loose wire ends just to be safe, but plugging it in now does *not* cause the breaker to flip and the oven clock turns on, etc.

thank you all!

So for now I can put the broke light socket back in so there isn't a gaping hole in the back of the oven and we can at least use the stove.

I would guess that my generic black wire tape is not rated for the temps that running the oven (not the stove burners) might create, rite? So we'll continue to not use the oven for now...


I still kinda want a new oven with a convection feature though :(

other people fucked around with this message at 19:07 on May 21, 2017

minivanmegafun
Jul 27, 2004

other people posted:

also, ebay had TWO sockets for less than the cost of one at other places but then i have to deal with weird ebay people and what would i do with two???

Welcome to the wild world of diy appliance repair, you end up buying parts from weird seemingly fly-by-night websites that amazingly deliver.

If you ever need vacuum cleaner parts (I have a 30-year old Electrolux I'll keep running until the motor finally goes kaput) Hesco is great.

Guy Axlerod
Dec 29, 2008
Buy the pair and sell the other for $1 as a service to your fellow man.

devicenull
May 30, 2007

Grimey Drawer

other people posted:

ohhhh. I could just tape over the end of the wires for the socket and put it back together?

i'll try this..


also, ebay had TWO sockets for less than the cost of one at other places but then i have to deal with weird ebay people and what would i do with two???



edit: it works! i taped over the loose wire ends just to be safe, but plugging it in now does *not* cause the breaker to flip and the oven clock turns on, etc.

thank you all!

So for now I can put the broke light socket back in so there isn't a gaping hole in the back of the oven and we can at least use the stove.

I would guess that my generic black wire tape is not rated for the temps that running the oven (not the stove burners) might create, rite? So we'll continue to not use the oven for now...


I still kinda want a new oven with a convection feature though :(

Lowes usually has a small section of weird bulb holders. I'm not sure if any of them are rated for oven temperatures.... but porcelain should hold up fine?

WashinMyGoat
Jan 15, 2002

angryrobots posted:

Garage receptacles are supposed to be gfci protected, so I bet you have a load wired gfci somewhere that is tripped (but doesn't look like it), or is bad.

Figure out which gfci is on the breaker that you believe powers the garage, and see if it's the problem.

So, I feel really dumb. The breaker is in a separate storage room in the garage. It never occurred to me to check for outlets in there. Sure enough, there was a GFCI outlet that was tripped behind a Christmas wreath.

The problem is solved, and I can spend the rest of my day relaxing and making up a story to tell my wife about how hard I worked to fix it.

MrYenko
Jun 18, 2012

#2 isn't ALWAYS bad...

WashinMyGoat posted:

...and I can spend the rest of my day relaxing and making up a story to tell my wife about how hard I worked to fix it.

This is the most challenging part of most home repair projects, honestly.

SoundMonkey
Apr 22, 2006

I just push buttons.


other people posted:

I would guess that my generic black wire tape is not rated for the temps that running the oven (not the stove burners) might create, rite? So we'll continue to not use the oven for now...

just since this wasn't addressed by anyone else, you are correct, that tape will absolutely not survive that

TooMuchAbstraction
Oct 14, 2012

I spent four years making
Waves of Steel
Hell yes I'm going to turn my avatar into an ad for it.
Fun Shoe
Refresher question on circuit load. Say I want to get a device that's rated at a 20A load (let's ignore what it's actual draw is, this is just its nominal draw). It's my understanding that to safely use such a device, I'd need it to be on a receptacle / circuit that was rated for at least 25% more amps, so that the device wouldn't exceed 80% of the circuit's capacity. Is that correct? If so, what even is the next step up from a 20A receptacle? I'd expect you'd normally go to 220V power at that point.

H110Hawk
Dec 28, 2006

TooMuchAbstraction posted:

Refresher question on circuit load. Say I want to get a device that's rated at a 20A load (let's ignore what it's actual draw is, this is just its nominal draw). It's my understanding that to safely use such a device, I'd need it to be on a receptacle / circuit that was rated for at least 25% more amps, so that the device wouldn't exceed 80% of the circuit's capacity. Is that correct? If so, what even is the next step up from a 20A receptacle? I'd expect you'd normally go to 220V power at that point.

I mean they sell 30A breakers, which gets you to 24A continuous load @ 110V. I bet there is a way to hardwire it into a dedicated single use circuit that lets you get away with cheaper components that the actual electricians would know about.

http://www.homedepot.com/p/Square-D-Homeline-30-Amp-Single-Pole-Circuit-Breaker-HOM130CP/202353319

TooMuchAbstraction
Oct 14, 2012

I spent four years making
Waves of Steel
Hell yes I'm going to turn my avatar into an ad for it.
Fun Shoe

H110Hawk posted:

I mean they sell 30A breakers, which gets you to 24A continuous load @ 110V. I bet there is a way to hardwire it into a dedicated single use circuit that lets you get away with cheaper components that the actual electricians would know about.

http://www.homedepot.com/p/Square-D-Homeline-30-Amp-Single-Pole-Circuit-Breaker-HOM130CP/202353319

Yeah, breakers aren't really the problem, it's the receptacle. I'd rather not hardwire the dust collector, because I want to be able to wheel it close to whatever tool needs it at the time I need it, instead of having the collector be stationary and running hoses all over the place.

Is my understanding correct, though, that a device listed as drawing 20A can't be put on a 20A circuit/receptacle?

glynnenstein
Feb 18, 2014


IIRC, the dust collector probably doesn't qualify as a continuous load, so you can use 100% of the circuit rating (at least if it's alone on the circuit). Ianae, so double check behind me and read the definition of continuous and non-continuous loads and what your equipment will be doing and for how long.

shame on an IGA
Apr 8, 2005

TooMuchAbstraction posted:

Refresher question on circuit load. Say I want to get a device that's rated at a 20A load (let's ignore what it's actual draw is, this is just its nominal draw). It's my understanding that to safely use such a device, I'd need it to be on a receptacle / circuit that was rated for at least 25% more amps, so that the device wouldn't exceed 80% of the circuit's capacity. Is that correct? If so, what even is the next step up from a 20A receptacle? I'd expect you'd normally go to 220V power at that point.

Sticking with 120VAC, the bigger straight blade plug/receptacle combinations will be NEMA 5-30 and 5-50 rated for 30 and 50 amps respectively. Twist lock connectors are available at 15, 20, 30, 50, and 60A ratings but at that point you'd be silly not to step up to 240v.

TooMuchAbstraction
Oct 14, 2012

I spent four years making
Waves of Steel
Hell yes I'm going to turn my avatar into an ad for it.
Fun Shoe

shame on an IGA posted:

Sticking with 120VAC, the bigger straight blade plug/receptacle combinations will be NEMA 5-30 and 5-50 rated for 30 and 50 amps respectively. Twist lock connectors are available at 15, 20, 30, 50, and 60A ratings but at that point you'd be silly not to step up to 240v.

Okay, good to know.

I suspect I'm just worrying over nothing and when the thing arrives I'll find that it has a standard 15A or 20A plug, but if it doesn't, then I'll know what to do about it.

Even if it is 15A-compatible, I'll probably still want to run a new circuit, because all of my overhead receptacles are currently on the same circuit, and they're by far the most convenient for running random tools. I suspect I shouldn't try to run the dust collector and, say, my miter saw at the same time on the same circuit.

H110Hawk
Dec 28, 2006

TooMuchAbstraction posted:

Okay, good to know.

I suspect I'm just worrying over nothing and when the thing arrives I'll find that it has a standard 15A or 20A plug, but if it doesn't, then I'll know what to do about it.

Even if it is 15A-compatible, I'll probably still want to run a new circuit, because all of my overhead receptacles are currently on the same circuit, and they're by far the most convenient for running random tools. I suspect I shouldn't try to run the dust collector and, say, my miter saw at the same time on the same circuit.

Just make sure that you get the dust collector up to speed, then the miter up to speed, then apply load nice and easy like. You can gently get breakers past their rating so long as you ease into it. There are all kinds of innuendos to make in conjunction with this description.

SoundMonkey
Apr 22, 2006

I just push buttons.


i'm having a ductless mini-split air conditioner installed soon. well i think am, the dude's coming today to have a look at the place.

no matter what i do the electrician's gonna have to pull a new circuit for it. there are 110 and 220V versions, the 110 is apparently totally functional and suitable for my space but slightly less efficient. the price is comparable, but the 220V one looks like a better unit. it's not actually meaningfully more expensive to have the electrician pull one than the other, is it, barring unforeseen fuckups?

H110Hawk
Dec 28, 2006

SoundMonkey posted:

i'm having a ductless mini-split air conditioner installed soon. well i think am, the dude's coming today to have a look at the place.

no matter what i do the electrician's gonna have to pull a new circuit for it. there are 110 and 220V versions, the 110 is apparently totally functional and suitable for my space but slightly less efficient. the price is comparable, but the 220V one looks like a better unit. it's not actually meaningfully more expensive to have the electrician pull one than the other, is it, barring unforeseen fuckups?

Marginally more materials costs should be all you incur, get the 220V one.

Blackbeer
Aug 13, 2007

well, well, well

SoundMonkey posted:

i'm having a ductless mini-split air conditioner installed soon. well i think am, the dude's coming today to have a look at the place.

no matter what i do the electrician's gonna have to pull a new circuit for it. there are 110 and 220V versions, the 110 is apparently totally functional and suitable for my space but slightly less efficient. the price is comparable, but the 220V one looks like a better unit. it's not actually meaningfully more expensive to have the electrician pull one than the other, is it, barring unforeseen fuckups?

It's possibly cheaper to go 220. I assume a large (maybe average?)mini-split needs more than 20amps @ 120V and would necessitate a #10/2wg run instead of #12. I've never installed one 120V, so check the unit max/fl amps. The breaker isn't much more expensive and the disconnect, whip, and install would all be the same price.

Blackbeer
Aug 13, 2007

well, well, well

TooMuchAbstraction posted:

Refresher question on circuit load. Say I want to get a device that's rated at a 20A load (let's ignore what it's actual draw is, this is just its nominal draw). It's my understanding that to safely use such a device, I'd need it to be on a receptacle / circuit that was rated for at least 25% more amps, so that the device wouldn't exceed 80% of the circuit's capacity. Is that correct? If so, what even is the next step up from a 20A receptacle? I'd expect you'd normally go to 220V power at that point.

Looked at the product page and it's hard to tell what they mean by 20amp. Are the full load amps 20.0? What's the service factor? Does the unit need a 20a plug? and etc. I hate when product page are vague like that. Looking at the instructions, it seems like it comes with a cord and plug pre-installed. Basically use whatever properly wired outlet fits the cord and hope they've made a good product. An efficient 2hp motor will use close to 20 amps, so I'd def plan on having it on by itself. If it's a unit that you'd wire yourself and you had the option, I'd rather wire it 240V than run bigger wire and use 30a twistlocks.

oh and glynnenstein is correct on it not being a continuous load

Blackbeer fucked around with this message at 03:25 on May 24, 2017

minivanmegafun
Jul 27, 2004

Are mini-splits worth considering if I'm in an area where natural gas is cheap? Do mini-splits that do gas heat and electric a/c exist?

Blackbeer
Aug 13, 2007

well, well, well

minivanmegafun posted:

Are mini-splits worth considering if I'm in an area where natural gas is cheap? Do mini-splits that do gas heat and electric a/c exist?

No duel units that I know of. They're fine for area cooling, but the heat pump would probably be a waste if you're installed for cheap gas. Just spitballing, but I assume heat pump vs cheap gas probably doesn't justify the install without decent local electric company rebates.

Blackbeer fucked around with this message at 03:36 on May 24, 2017

SoundMonkey
Apr 22, 2006

I just push buttons.


i figure i'll use mine for heat in the cool-but-not-cold months, but otherwise use the gas furnace

knowonecanknow
Apr 19, 2009

Ambition must be made to counteract ambition.
At my work all the face plate screws are oriented vertically. Is this a thing or just OCD?

TooMuchAbstraction
Oct 14, 2012

I spent four years making
Waves of Steel
Hell yes I'm going to turn my avatar into an ad for it.
Fun Shoe

knowonecanknow posted:

At my work all the face plate screws are oriented vertically. Is this a thing or just OCD?

You mean, like, the slots in the screw heads are all aligned? That's gotta be OCD.

knowonecanknow
Apr 19, 2009

Ambition must be made to counteract ambition.

TooMuchAbstraction posted:

You mean, like, the slots in the screw heads are all aligned? That's gotta be OCD.

Yeah that, I figured OCD but wasn't sure.

Bad Munki
Nov 4, 2008

We're all mad here.


Besides, everyone knows they're better with the slot horizontal.

Hubis
May 18, 2003

Boy, I wish we had one of those doomsday machines...
This reminds me: Ground Up or Ground Down? Apparently people have "opinions" about this.

Bad Munki
Nov 4, 2008

We're all mad here.


I believe the intended design is ground up, such that if something fell across a partially-inserted plug, it would hit the ground first.

That being said, ground down is obviously the residential de facto standard, at least as far as a 5-15 goes.

Not Wolverine
Jul 1, 2007
Depends on if you want a direct short between hot and neutral or a 50/50 chance of a hot or neutral to ground short for the one time in your life that a plug is loose enough for a knife to slip in behind the plug yet still far enough in to make contact. . .

I have never seen neutral on top outside of a hospital so I would go with ground down. Aligning the screw heads is just straight up OCD and a resentment for properly tightened fasteners.

other people
Jun 27, 2004
Associate Christ
which part is ocd, putting them in like that or noticing they are in like that?

H110Hawk
Dec 28, 2006

other people posted:

which part is ocd, putting them in like that or noticing they are in like that?

Yes.

glynnenstein
Feb 18, 2014


Ground down. Easier to line up the bent prongs on some old tool.

Adbot
ADBOT LOVES YOU

babyeatingpsychopath
Oct 28, 2000
Forum Veteran


knowonecanknow posted:

At my work all the face plate screws are oriented vertically. Is this a thing or just OCD?

That's a sign of a craftsman taking pride in their work. Someone went through and deliberately made sure that the screws were appropriately tight, and aligned. Probably also made sure the switch plate was plumb (or at least square with the nearest "vertical" edge).

Hubis posted:

This reminds me: Ground Up or Ground Down? Apparently people have "opinions" about this.


Hubis posted:

This reminds me: Ground Up or Ground Down? Apparently people have "opinions" about this.

1) Follow what the spec says. If the spec says ground up, do that. If it says ground down, do that.
2) Failing that: Ground down in residential (or match everything else in the room) and ground up in commercial.
3) Failing that: Do it all exactly the same. That way, when the customer says 'hey this outlet is upside down' you can say 'every outlet in the building is like that.'

Any reasons why one way is "better" is just legend -- flooding, things falling across prongs, ants, how Westinghouse was left-handed so that prong goes there, etc.