asdf32 posted:Heh, I actually just added one of those to my attic last weekend, it already had 2 and I wanted a 3rd. Are they legal in the attic? What kind of $5-$10 fixture are you talking about? National Electric Code posted:110.27.(B) Prevent Physical Damage. In locations where electrical equipment is likely to be exposed to physical damage, enclosures or guards shall be arranged and of such strength as to prevent such damage. Nothing wrong with using incandescents in an attic or rarely used basement. Unless you live in CA where it's illegal, but even then it's still kinda stupid to spend an extra $2 on a bulb to save maybe 2 cents in electricity. You *may* have issues with flourescent lights taking a while to turn on in your garage on cold mornings, but I've never really had problems in my garage. My unheated shed- yes, takes a long time to heat up, but not the garage. YMMV. FYI, enclosed CFLs (like floodlights and recessed lights) take a lot longer to warm up than open CFL fixtures, so definitely don't use them in cold areas. grover fucked around with this message at 02:38 on Jan 27, 2013 |
# ¿ Jan 27, 2013 02:29 |
|
|
# ¿ May 19, 2024 23:36 |
|
Bad Munki posted:My house was built in 2007 and it had three of those fixtures in the garage; it's not a junker house or anything, quite the opposite. I suspect that "likely to be exposed to physical damage" is highly subjective.
|
# ¿ Jan 27, 2013 02:39 |
|
babyeatingpsychopath posted:Anything over 6'6" is not readily accessible, therefore protected from physical damage. Unfinished and/or uninhabitable spaces that do not get regular use = no physical damage. Attics are another funny one. If it's not used for storage, bare bulbs are OK. Throw a box in the attic, though? Now it's subject to damage. Seems to be a common convenient discrepancy- builder claim's it's not used for storage and cheaps out on the fixture to save $3, but what's the first thing the homeowner does? Toss some scrap plywood over the joists and fill 'er up. I wonder how many homes burn down when a cardboard box crushes a bulb and lights off?
|
# ¿ Jan 27, 2013 04:35 |
|
Bad Munki posted:I need that but for a 4' fluorescent fixture...preferably something that can be mounted I guess on the sheetrock? I saw one product on the web with a 5" width and 4" depth that I think would work, it seems to be the same thing sold pretty much everywhere, but I can't really tell how it actually mounts. Or, for $20, you could just get a new fixture.
|
# ¿ Jan 27, 2013 16:36 |
|
Pufflekins posted:gently caress 750 kcmil teck cable. It's a bitch.
|
# ¿ Feb 14, 2013 00:36 |
|
Pufflekins posted:There is, however, a bunch in these dorms we're wiring
|
# ¿ Feb 14, 2013 02:50 |
|
Cpt.Wacky posted:I don't know, that's what Home Depot is selling for 2 bulb 4 foot direct wire flush mount with diffuser. Maybe it's a cost saving measure to save a few cents on wire? I could see series wiring being a problem with 4 bulbs but 2 is easier to test.
|
# ¿ Feb 15, 2013 00:31 |
|
kid sinister posted:That really comes down to amperage. All USB uses 5V DC. According to specs, any USB port that handles data is limited to a max of 0.5A under USB 2.0 and 0.9A under 3.0, at least when data is being sent back and forth. The newest Apple plug-in USB charger is rated for 12W. Apply a little Watt's Law and it puts out 2.4A. Only happened once; I forget what I was doing, but it was an aberration. Still, these can be high-drain devices.
|
# ¿ Feb 27, 2013 03:48 |
|
IOwnCalculus posted:In general, what is code like for running conduit / outside outlets? My HOA can be intermittently anal-retentive, but I'm thinking it would be relatively easy to run conduit down to just above ground level, flush up against the outside of the house, and then come back up to a reasonable height and stick the outlet at the front of the driveway where I currently have a broken garage door keypad. Or can I trench it and come up at the driveway? Or am I going to be paying an electrician to crawl around in my attic space and fish cabling over the front bedroom to drop the outlet along the inside wall of the garage, near the garage door? You could always run oversized cable, which would give you an easy upgrade path, should you change your mind in the future and want to use a 6.6kW charger. grover fucked around with this message at 12:42 on Mar 4, 2013 |
# ¿ Mar 4, 2013 12:38 |
|
oldskool posted:Speaking of running oversized cable, is it possible to use 15A outlets with 10ga wire? It's not the outlets I'm having trouble with, it's the lovely mobile home circuitry that has half the kitchen, the office & the spare bedroom's lights & outlets all sharing one 15A breaker & I'd prefer to replace as little as possible to make it so I can microwave without shutting off the office computer & the lights. IOwnCalculus posted:It's funny, I never even thought about trenching it until I wrote up that post, and that's probably the most sane way to do it since I think the HOA would probably be annoyed at any not strictly necessary additional conduit on the front of the house, even if it's nearly 100% invisible from the street by running at ground level. grover fucked around with this message at 18:37 on Mar 4, 2013 |
# ¿ Mar 4, 2013 18:31 |
|
oldskool posted:3) Go fixture-by-fixture back towards the box, replacing the 14ga wire with 10ga as I go. And yeah, you don't want the microwave, space heater and AC units on the same breaker; they'll each pull damned close to 15A by themselves and will quickly overload it. To do it right, you're going to need to add more circuits. The AC won't ever be on the same time as the space heater (right?) so you can potentially share a circuit there. Still leaves you with 3 dedicated circuits if you want to eliminate overload trips. Can you use tandem breakers to effectively increase the # of breakers in your panel, are they available for your panel?
|
# ¿ Mar 4, 2013 21:09 |
|
oldskool posted:I've got tandem breakers installed at the moment, but I might be maxed out. I'll have to check the diagram.
|
# ¿ Mar 4, 2013 22:03 |
|
stik posted:I'm trying to not involve real electricians because they may tell me I need to replace all of my wiring and that's not an option right now. I do plan on rewiring the entire house this fall but for now it isn't going to happen. Fair warning: if you replace your panel and don't upgrade the house to 100% grounded wiring, 2x20A GFCI circuits in the kitchen, etc., your locality may fail you on inspection and make you do it anyhow. Depends on your locality- I highly recommend you call them and explain the situation and ask what their policy is for this sort of thing. They *might* grant you some leniency as a properly done panel without those upgrades is safer than the old panel without those upgrades, but the last thing you want to happen is a failed inspection and your power gets shut off until you fix it. Upgrade it without inspection, and your insurance company may not pay out if your house burns down. grover fucked around with this message at 22:06 on Mar 10, 2013 |
# ¿ Mar 10, 2013 22:04 |
|
Account_Username posted:Does every type of electrical work have to be inspected? I replaced a beat-up 15 amp outlet with a new one myself a few weeks ago.
|
# ¿ Mar 11, 2013 02:10 |
|
stik posted:Well I'm just replacing one box with another so I should be good. San Antonio is extremely lax about this kind of thing compared to other parts of the country too luckily.
|
# ¿ Mar 11, 2013 02:45 |
|
Account_Username posted:So is it not normal to have an outside breaker then? There is a panel outside mounted on the same post as the kwh meter to cut off power going into the house where I live. It only has a main breaker + some other breaker in it, all breakers for individual circuits are in the panel inside the house. Every house in the neighborhood is like this, so I don't think ours is an outlier. Would it be because we live in a mobile home (trailer)?
|
# ¿ Mar 11, 2013 23:19 |
|
IOwnCalculus posted:The fact that it's outside isn't at all unusual, at least to me. In AZ every house I've lived in has the main panel on the outside with the meter; the only times I've had electrical panels indoors have been apartments. Shameless plug for my generator thread, btw: http://forums.somethingawful.com/showthread.php?threadid=3515309
|
# ¿ Mar 11, 2013 23:54 |
|
Nuntius posted:Not sure if this is the best place to ask this, but it seems roughly right. grover fucked around with this message at 01:47 on Mar 15, 2013 |
# ¿ Mar 15, 2013 01:44 |
|
Be careful when attempting to install UF by putting it in the conduit before you install the conduit. Sure, you avoid having to pull it through, but PVC cement will damage UF insulation.
grover fucked around with this message at 01:43 on Mar 21, 2013 |
# ¿ Mar 21, 2013 01:40 |
|
particle409 posted:Can you just throw some strong fishing line in the conduit before installation? Then you just tape/attach one end of the line to your UF, and pull it through. Like this, but smaller: https://www.youtube.com/watch?v=sMA9ybAtpzo Other tips: http://electrical.about.com/b/2011/08/22/how-do-i-pull-wire-through-conduit.htm grover fucked around with this message at 15:01 on Mar 31, 2013 |
# ¿ Mar 31, 2013 14:56 |
|
kid sinister posted:What are those plugs on the end for?
|
# ¿ May 4, 2013 20:04 |
|
Noctone posted:To add on to both of these posts, cam-locks are primarily used for temporary three-phase power feeds. Probably the most common application I see is to connect a load bank to a generator. We also use them quite regularly at work to feed 480 or 208 to our breaker test sets.
|
# ¿ May 6, 2013 00:51 |
|
Those 2-prong adapters are unsafe and illegal to use in this way. There are only two safe and legal ways to plug 3-prong grounded appliances & equipment into 2-prong outlets: 1) Upgrade it to an actual grounded 3-prong outlet by pulling in a new ground wire. If you're REALLY lucky, the ground is already in the box, and all you have to do is hook it up. I've yet to see it, though. 2) You can install a GFCI receptacle on the circuit, which will allow you to legally install 3-prong receptacles on all downstream outlets that are protected by it. It still won't be grounded, but the GFCI provides shock protection and allows for this in the electrical code. This must be labeled "UNGROUNDED" and "GFCI PROTECTED"
|
# ¿ May 9, 2013 01:08 |
|
kid sinister posted:My own house was! Well, half of it. Half the house the original electrician twisted the grounds together outside the boxes and attached them to a box gang screw, the other half he clipped the ground off where he removed the outer insulation. That's when I got double lucky and the ground wire was bent zigzagged inside the outer sheath so I was able to tug out an inch to twist pigtails onto.
|
# ¿ May 9, 2013 10:47 |
|
SneakyBeef posted:Nope, I believe the max is 8 receptacles if you want to maintain the UL listing for their purpose. I'm sure it will tell you just how many on the instruction sheet that comes in the box though. Missed the apartment bit; yeah, you can't do poo poo like this no matter how much it makes sense if you're renting, sorry. GFCI power strip'll have to do.
|
# ¿ May 10, 2013 01:51 |
|
Cat Hatter posted:I tried pulling it out with pliers but it's broken off flush with the socket it pushes into.
|
# ¿ May 20, 2013 15:03 |
|
Laminator posted:Okay, sounds good. I'll get a new gfci and see if I can grab a new gasket. Maybe a bead of caulk around the outside of the case would help?
|
# ¿ Jun 7, 2013 17:32 |
|
Cat Hatter posted:I'm too lazy to try another brand yet because then I'd have to go to a different store, but the last time I picked one up I got a regular bulb because they're built a bit different from the double-life bulbs that I've been using. I was actually wondering if anyone knows why the normal bulbs have a sort of doughnut-hole in the middle of them? I've never seen anything like it in a light bulb before.
|
# ¿ Jun 10, 2013 10:47 |
|
ShadowStalker posted:I'd add the outlet. A retrofit box and outlet will cost less than $5 and won't take too much time to do.
|
# ¿ Jun 13, 2013 10:48 |
|
FCKGW posted:My coworker installed a new Nissan Leaf charger, not sure if he has the wiring done right or not. 1. Needs to be stapled within 12" of the box 2. Needs to have a protective grommet with strain relief where it enters the box (maybe there is one? can't tell) 3. The insulation should be stripped and cut trim within 1/4" or so if where it enters the box, not hanging out like that. 4. Can't tell what he did inside the receptacle box, but it doesn't look like the box is hung properly 5. The receptacle box needs a strain relief grommet 6. The wire is supposed to be stapled within 12" of this, too. Basically, you need another 50 cents worth of fittings, a couple staples, and some decent worksmanship to make this code-legal. The white romex coming out of that box looks awful, too.
|
# ¿ Jun 25, 2013 01:33 |
|
Depends on what the actual brand is. If it's a Cooper combo switch it should have a break-off tab and is even easier; black on black, white to silver and red to copper, and no jumpers necessary. If it doesn't have a tab, yeah, you need to pigtail it. Would make more sense if they all had tabs; pretty just exactly what they're made for. grover fucked around with this message at 21:29 on Jul 15, 2013 |
# ¿ Jul 15, 2013 21:11 |
|
Astonishing Wang posted:I already broke the tab off, I was just a little thrown because I need one more wire than I have. I can just take off the wire nut and use the two black lines as they are, correct?
|
# ¿ Jul 15, 2013 23:10 |
|
dietcokefiend posted:I need to get a UPS working in another room, only problem is the room doesn't have the proper outlet. Is there anything wrong with putting a L5-30R outlet on a 20A circuit? Breaker is still a 20A breaker and the UPS wouldnt be drawing more than 20A. Is it breaking code by doing this?
|
# ¿ Jul 20, 2013 13:26 |
|
FogHelmut posted:I'm installing a light in my ceiling, and above my ceiling there is like a truss similar to this: grover fucked around with this message at 19:44 on Jul 20, 2013 |
# ¿ Jul 20, 2013 19:40 |
|
UF is a lot like romex, only it's solid rubber jacket instead of a thin rubber sheath with paper filler like NM-B. Data on NM-B cable is printed on the jacked, but UF is stamped- if it's UF, you should be able to see it through the paint. If you can't tell, open the GFCI receptacle and look at the termination.Motronic posted:Previous Owner.
|
# ¿ Jul 21, 2013 11:00 |
|
Motronic posted:The gray area isn't about the moisture resistance, it's about lack of abrasion resistance in a cable who's abrasion resistance is supposed to be supplemented by 12" of soil or by being behind drywall or in a conduit. grover fucked around with this message at 23:53 on Jul 21, 2013 |
# ¿ Jul 21, 2013 23:49 |
|
SuicidalSmurf posted:Going crazy trying to replace a breaker with a GFCI breaker. I am confident I have found the neutral/hot pair that go to the circuit I want to protect, and I properly connected the neutral off the breaker to the neutral bus. When I try and power on the circuit it instantly trips. Is it possible I have the wrong neutral? When I was troubleshooting, I attempted disconnecting various neutrals one at a time from the panel in an attempt to verify I was working with the correct neutral, and I had the lights stay on on that circuit regardless of the neutrals being disconnected. Is this normal? If this is the case, you need to start opening all the downstream boxes to figure out where the neutral-ground fault is. Considering your lights stay on with this neutral wire lifed, I suspect this neutral is wired up to another neutral circuit somewhere- I'd start looking in light switches, especially any gang boxes with more than one light switch in them. grover fucked around with this message at 22:24 on Jul 29, 2013 |
# ¿ Jul 29, 2013 22:22 |
|
SuicidalSmurf posted:Makes sense. I know in the bathroom the neutral in the switch is tied to two other neutrals I believe. So if one of the neutrals it is tied into is on another circuit/breaker that would cause the fault?
|
# ¿ Jul 29, 2013 22:57 |
|
Couple bits of code: * You need to put a service-rater breaker between the meter and the ATS. * The neutral must be bonded once, and only once in the system. If it's a 2-pole ATS, you'll need to float the neutral-ground bond in the generator and bond it ONLY at the ATS or main panel. (3-pole will switch the neutral.) * If you have an ATS, your generator is required to be sized for 100% of your loads. In other words, really big. If you have a reasonably sized generator, you can only have an MTS. * You need working space for the ATS and panel. It must be 36" deep and 30" wide. It doesn't matter if the 30" is centered on the panel or begins at the edge of it, so long as you have a 30" wide working space to get into it. grover fucked around with this message at 17:51 on Aug 10, 2013 |
# ¿ Aug 10, 2013 03:52 |
|
|
# ¿ May 19, 2024 23:36 |
|
He's in europe, so their conduit sizes and names are different. I'd imagine 30, 40 and 50mm flexible conduit are available for this type of use.babyeatingpsychopath posted:To further complicate things, if your ATS doesn't switch the neutral (most residential don't), then the neutral-ground bond is inside your main panel, only. You're forever and ever completely forbidden from ever allowing your generator to run when there's ever any possibility at all in any possible way of energizing the utility, no matter how remotely. Usually, this means some kind of locking cam inside your ATS that only your utility company is allowed to have keys for. If power drops, it's up to them to unlock your ATS for you to get back on the grid; until then, you're pouring gas in your generator to keep your steaks chilled. In this case, he'd have to have a service disconnect breaker right after the meter, which is where the neutral-ground bond should be. The only difference between a switched neutral and hardwired neutral is whether the generator has its own N-G bond. Code permits either method. My recommendation is to hook up the generator to a 2-pole breaker on the main panel with a sliding sheet-metal interlock to prevent both the generator and main breaker from being simultaneously closed; simple, as effective as an MTS, code-legal, and dirt cheap. grover fucked around with this message at 18:05 on Aug 10, 2013 |
# ¿ Aug 10, 2013 18:00 |