You can: log in, read the tech support FAQ, or request your lost password. This dumb message (and those ads) will appear on every screen until you register! Get rid of this crap by registering your own SA Forums Account and joining roughly 150,000 Goons, for the one-time price of $9.95! We charge money because it costs us money per month for bills, and since we don't believe in showing ads to our users, we try to make the money back through forum registrations.
 
  • Locked thread
helno
Jun 19, 2003

hmm now were did I leave that plane
We have similar failed fuel detection systems. CANDU reactors monitor the individual fuel channels for delayed nuetrons to detect failed fuel. If it is detected we simply fuel that channel till we have removed the failed bundle.

Boiler tube inspection and plugging is a massive outage job and I am sure it is similar at all PWR reactors.

As to water chemistry we get the added bonus of our PHT and Moderator water containing tritium. We spend alot of time in positive pressure suits to avoid that.

Luckily I work mostly on the turbines so I spend very little time "in the bag".

Adbot
ADBOT LOVES YOU

a rowdy mullet
Feb 12, 2009
Just wanted to chime in, I work for a large utility on the West Coast, but I'm not exposed to any of the wonderful engineering grid stuff since I work in Energy Efficiency. "Need to know basis" and all :(.

Luckily, it's an awesome place to work, and it's surprisingly interesting being on the inside of a utility.

This thread is really interesting, it makes me want to tour the gas turbine plant near my office even more :f5:

Frozen Horse
Aug 6, 2007
Just a humble wandering street philosopher.

helno posted:

As to water chemistry we get the added bonus of our PHT and Moderator water containing tritium. We spend alot of time in positive pressure suits to avoid that.

Look on the bright side, it's not a graphite-moderated reactor. My pet favourite nuclear reactor design (not yet implemented AFAIK), remains the sub-critical accelerator-driven energy amplifier.

modig
Aug 20, 2002

ANIME AKBAR posted:

Just curious, is he doing prepolarized MRI?

Yeah.

Nerobro
Nov 4, 2005

Rider now with 100% more titanium!

Frozen Horse posted:

Look on the bright side, it's not a graphite-moderated reactor. My pet favourite nuclear reactor design (not yet implemented AFAIK), remains the sub-critical accelerator-driven energy amplifier.

Chernobyl. That design was (is... as it's still running in some places in the eastern bloc...) at least partially moderated by graphite.

CP1 was graphite moderated. http://en.wikipedia.org/wiki/Chicago_Pile-1 So were most of the air cooled reactors. http://en.wikipedia.org/wiki/X-10_Graphite_Reactor

Graphite as a moderator is scary.

http://en.wikipedia.org/wiki/Windscale_fire

Groda
Mar 17, 2005

Hair Elf

helno posted:

Boiler tube inspection and plugging is a massive outage job and I am sure it is similar at all PWR reactors.

How bad does Canada want the Bomb that they still deal with these?

helno
Jun 19, 2003

hmm now were did I leave that plane
It would actually be pretty tricky to do in one of our power reactors.

The candu design is mostly a throwback to a time when we couldn't make the pressure vessels needed for a PWR so we designed around it. That then became the trademark of our design. Edit: We also dont have any fuel enrichment facilities due to our lack of a weapons program so running on natural uranium was a plus.

Sadly it will probably never be built again now that the reactor division of AECL just got sold to SNC-Lavlin. That sale essentially gave SNC-Lavlin a few million dollars to lay off about 1000 engineers at AECL.

Three-Phase
Aug 5, 2006

by zen death robot
Cool video I found: showing the magnetic forces involved in a serious electrical fault. From Ferraz-Shawmut.

http://www.youtube.com/watch?v=pSxqVh2RYGU

Also, Kaboom! (I don't think he was hurt. Much.) Pulling fuse while current was flowing perhaps?
http://www.youtube.com/watch?v=ZjXK8Vhm4Po

There are some amazingly dangerous videos on YouTube of kids playing with pole transformers they wired up backwards, too.

Speaking of danger...

http://www.youtube.com/watch?v=uDB0t5ZL_p0

Shouldn't this guy:
1. Be wearing the outer protective gloves and not wearing just the inner portion
2. Be wearing arc-flash gear

This looks to me like an electrical accident waiting to happen.

Three-Phase fucked around with this message at 01:41 on Sep 24, 2011

movax
Aug 30, 2008

What's a good nuclear engineering textbook you guys used in school? Wikipedia's nice, but I'd like a book I can read to improve my knowledge of the reactor types and keep them straight in my head.

grover
Jan 23, 2002

PEW PEW PEW
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:

Three-Phase posted:

Cool video I found: showing the magnetic forces involved in a serious electrical fault. From Ferraz-Shawmut.

http://www.youtube.com/watch?v=pSxqVh2RYGU
I've often heard this could happen and have seen it in video, but had never seen it first-hand until one of the contractors I work with mis-wired a load bank- essentially feeding the full output of a 480V 400kVA transformer into a pair of 30' long #12 control wires. Damned things whipped like crazy! The 2A fuse blew almost instantly, but the magnetic forces from that much instantaneous current was amazing.

Frozen Horse
Aug 6, 2007
Just a humble wandering street philosopher.
That's a very interesting video. How do current-limiting breakers and fuses work? As I understand it, a regular fuse is a length of wire made of a low-melting alloy with sufficient resistance so that it will melt due to resistive heating above its rated current. Other added tricks involve the wire being under spring tension to widen the gap rapidly to prevent arcing. What gets added to give it magic current-limiting powers? If it's just a 1-ohm resistor in series, I'm going to be disappointed.

shame on an IGA
Apr 8, 2005

Frozen Horse posted:

That's a very interesting video. How do current-limiting breakers and fuses work? As I understand it, a regular fuse is a length of wire made of a low-melting alloy with sufficient resistance so that it will melt due to resistive heating above its rated current. Other added tricks involve the wire being under spring tension to widen the gap rapidly to prevent arcing. What gets added to give it magic current-limiting powers? If it's just a 1-ohm resistor in series, I'm going to be disappointed.

They just work faster. All "current limiting" means, in the context of breakers and fuses, is that they interrupt the circuit and extinguish the arc within 1/2 of a cycle from the beginning of the fault.

Groda
Mar 17, 2005

Hair Elf

movax posted:

What's a good nuclear engineering textbook you guys used in school? Wikipedia's nice, but I'd like a book I can read to improve my knowledge of the reactor types and keep them straight in my head.

I don't think I had a single generally available nuclear engineering textbook my entire program!

What are you interested in? Mechanical engineering? Physics?

Three-Phase
Aug 5, 2006

by zen death robot

The Proc posted:

They just work faster. All "current limiting" means, in the context of breakers and fuses, is that they interrupt the circuit and extinguish the arc within 1/2 of a cycle from the beginning of the fault.

One point - some fuses are "dual element" fuses. They have two separate parts - they have a mechanism that will blow during a sustained overload, and they also have a series of links that will blow in a very serious high-current fault.

As far as whipping, I've heard stories about situations where there was a "triplex" bundle of wires in a cable tray, just three wires bundled together every few feet with those really thick tie-wraps. There was a fault and over a half-mile of cable every tie wrap was broken.

Also, compared to circuit breakers, fuses have very specific trip curves so you can accurately predict when they'll blow, and that also makes coordination easier.

Three-Phase fucked around with this message at 12:11 on Sep 24, 2011

grover
Jan 23, 2002

PEW PEW PEW
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
Here are some photos of a blown industrial current-limiting 315A fuse. And yes, it's full of sand, ordinary silica sand, which is used to extinguish the arc quicker.





The trip curves for this fuse are on page 61 here, the set on the right. You can see how different the trip curve looks when compared to a typical circuit breaker of the same size.

DaveSauce
Feb 15, 2004

Oh, how awkward.

Three-Phase posted:

Cool video I found: showing the magnetic forces involved in a serious electrical fault. From Ferraz-Shawmut.

http://www.youtube.com/watch?v=pSxqVh2RYGU


Bussmann showed us a similar video when they were in our building for SCCR training. They also showed other effects of not properly protecting things. I can't find the videos online, but they basically showed different breakers and fuses blowing with different interrupting ratings. The class J fuses blew, and the circuit breakers blew up. I'm betting that the 2nd video you posted was someone shorting something in the panel on accident and the protective device wasn't rated for the available fault current.

On that note, how common is proper coordination? I'm a controls engineer for a panel shop and I handle one of our larger OEM accounts. We almost never talk to the end user, and just about every panel we build for them is rated for 5kA. We've been putting it on every proposal since we got our SCCR training I mentioned above early this summer (we tried it once before the training but the OEM yelled at us because customers were asking questions...). Since then, I think I've had to design 1 panel that met 75kA. Nobody else has mentioned anything. I'm a little worried that something like this video is going to happen to some poor electrician out in the field, but it's drat expensive to meet these ratings when the OEM gives us peanuts for these panels.

And I actually still have questions about SCCR. Am I correct in saying that a combination rating must be tested by UL (i.e. class J fuse in front of a contactor) for it to be valid? Or can I just put a 200kA rated class J fuse with a 5kA let-through in front of a 5kA rated contactor and call it 200kA?

I ask this because it's drat near impossible to find properly rated combinations without buying a load of unnecessary equipment. I don't want to buy a $2000 molded case switch to protect a 5HP motor starter when I can use a couple J fuses and a 200kA rated disconnect, but a lot of manufacturers have wacky combinations listed for higher SCCRs.

grover
Jan 23, 2002

PEW PEW PEW
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:
:circlefap::circlefap::circlefap:

DaveSauce posted:

And I actually still have questions about SCCR. Am I correct in saying that a combination rating must be tested by UL (i.e. class J fuse in front of a contactor) for it to be valid? Or can I just put a 200kA rated class J fuse with a 5kA let-through in front of a 5kA rated contactor and call it 200kA?

I ask this because it's drat near impossible to find properly rated combinations without buying a load of unnecessary equipment. I don't want to buy a $2000 molded case switch to protect a 5HP motor starter when I can use a couple J fuses and a 200kA rated disconnect, but a lot of manufacturers have wacky combinations listed for higher SCCRs.
A breaker/fuse does not need to have a high-enough interrupt rating if there is a properly sized breaker/fuse upstream, but it still needs to be series-rated for the available arc-fault current. If that system can push 200kA through it, it needs to be rated for it. This may mean you need to install isolation transformers other fault current-limiting devices in some situations.

freeforumuser
Aug 11, 2007
What is difference between 3-phase 415V vs residential 1-phase 230V mains? What are the reasons they are used as it is?

Ossetepo
Mar 12, 2011

movax posted:

What's a good nuclear engineering textbook you guys used in school? Wikipedia's nice, but I'd like a book I can read to improve my knowledge of the reactor types and keep them straight in my head.

Like the other guy said, there aren't any good NukeE textbooks. That said, if you're just looking for a basic introduction to reactor technology, http://www.amazon.com/Nuclear-Engineering-Handbook-Mechanical-Aerospace/dp/1420053906/ref=sr_1_5?ie=UTF8&qid=1317083893&sr=8-5 isn't terrible, as long as you're already fluent in engineer-ese. It's got a decent overview of the major western-world reactors, some history of reactor and auxiliary systems design, and a little bit of reactor physics at the end. My degree is in chemistry, so it was one of the many books I read after coming to work in nuclear land to figure out how things actually work.

Ossetepo fucked around with this message at 01:58 on Sep 27, 2011

KaiserBen
Aug 11, 2007

Three-Phase posted:

Speaking of danger...

http://www.youtube.com/watch?v=uDB0t5ZL_p0

Shouldn't this guy:
1. Be wearing the outer protective gloves and not wearing just the inner portion
2. Be wearing arc-flash gear

This looks to me like an electrical accident waiting to happen.

Yes, he should. Speaking of electrical accidents, we've had a good one here lately. A guy was checking voltage on a new transformer (4160V->460V stepdown transformer), and he put a rotation meter (to check phase rotation) on the output, and then closed the breaker feeding it. Meter blows up. Then he puts his voltmeter on the output terminals (while holding it, not wearing all the gear, but had gloves and safety glasses, IIRC) and found out the hard way that it was a 4160->4160 isolation transformer, not a stepdown. Meter was a total loss. He was fine, but a bit shaken up.

ANIME AKBAR
Jan 25, 2007

afu~

modig posted:

Yeah.

Let me guess, Stanford?

If so you're lucky as hell to work with some of the best engineers in MRI. I'm jealous.

ANIME AKBAR fucked around with this message at 04:38 on Sep 27, 2011

modig
Aug 20, 2002

ANIME AKBAR posted:

Let me guess, Stanford?

If so you're lucky as hell to work with some of the best engineers in MRI. I'm jealous.

I think they were working on pre-polarizing high field MRI. This is low field MRI using room temperature magnets and cryogenic magnetic field measurements, instead of room temperature measurement and cryogenic magnets.

Three-Phase
Aug 5, 2006

by zen death robot

freeforumuser posted:

What is difference between 3-phase 415V vs residential 1-phase 230V mains? What are the reasons they are used as it is?

415? You're from Europe, right?

With a three-phase system you have three wires that have a potential between each other (A-B, B-C, C-A) and optionally a neutral (A-N, B-N, C-N) as a fourth wire.

With a (US) single-phase system, you have two 120V lines and a neutral, 120V from either line to neutral, and 240V between BOTH lines.

Three phase is generally used for larger applications - industrial, commercial, and power transmission.

KaiserBen posted:

Yes, he should. Speaking of electrical accidents, we've had a good one here lately. A guy was checking voltage on a new transformer (4160V->460V stepdown transformer), and he put a rotation meter (to check phase rotation) on the output, and then closed the breaker feeding it. Meter blows up. Then he puts his voltmeter on the output terminals (while holding it, not wearing all the gear, but had gloves and safety glasses, IIRC) and found out the hard way that it was a 4160->4160 isolation transformer, not a stepdown. Meter was a total loss. He was fine, but a bit shaken up.

Oops! He didn't check the nameplate?

SeaBass
Dec 30, 2003

NERRRRRRDS!

DaveSauce posted:

On that note, how common is proper coordination?

It is not as common as it should be, but with OSHA being more assertive about assessing arc flash hazards, design engineers will be more diligent about protective device evaluation and coordination. Or they can pay me to do it for them :)

Honestly, for all of the reports I have reviewed, less than half are done correctly and that is because the systems are so small there is little room for error. The larger the system, the more room for something to get overlooked or not considered as a fault current contribution.

Three-Phase
Aug 5, 2006

by zen death robot

SeaBass posted:

Honestly, for all of the reports I have reviewed, less than half are done correctly and that is because the systems are so small there is little room for error. The larger the system, the more room for something to get overlooked or not considered as a fault current contribution.

On our equipment we have bus protection relaying, so if there's a fault detected, not only does the bus' circuit breaker trip, but every large machine also connected to the bus simultaneously trips off as well. (I think that's an 86 relay.)

pazrs
Mar 27, 2005

Three-Phase posted:

415? You're from Europe, right?


Or Australasia.


Interesting thread, I love reading about all the hardware.

Anti-Hero
Feb 26, 2004

SeaBass posted:

It is not as common as it should be, but with OSHA being more assertive about assessing arc flash hazards, design engineers will be more diligent about protective device evaluation and coordination. Or they can pay me to do it for them :)

Honestly, for all of the reports I have reviewed, less than half are done correctly and that is because the systems are so small there is little room for error. The larger the system, the more room for something to get overlooked or not considered as a fault current contribution.

My experience with industrial coordination is much the same. Fuses coordinating with molded case breakers are incredibly rare. I'm more of a distribution/transmission protection engineer where coordination is generally pretty straight forward.

I recently worked on coordinating an industrial installation where all the 480V circuit breakers were UL short circuit rated, and not ANSI rated. The consequence of only performing UL testing is that a hard-coded instantaneous trip must present. If you perform ANSI tests you can dispense with this as you've proved the breaker won't fail to trip on a high enough fault current.

The result is that nothing was going to coordinate. It didn't matter if I set the LTPU, LTD, STPU, etc. of the main breaker to coordinate with the feeders, they all had something like a 10 kA non-defeatable inst. function, and the available fault current in the plant was much higher. So I noted in the report that they needed to stop being cheap bastards and replace all this gear with ANSI rated breakers because if they have a fault anywhere in the 480V system it was anyone's guess what was going to clear first. But this is protection, and no one cares about it until it doesn't work.

Anti-Hero
Feb 26, 2004

Three-Phase posted:

On our equipment we have bus protection relaying, so if there's a fault detected, not only does the bus' circuit breaker trip, but every large machine also connected to the bus simultaneously trips off as well. (I think that's an 86 relay.)

That is 87B protection. But what if you have a fault outside of that zone? Like on the cable between the machine and the switchgear bus? That's when proper coordination between upstream and downstream devices is critical, and where the most exposure to mis-coordination lies. This is where overlapping zones for differential protection is very helpful, especially in mitigating arc-flash incident energy levels.

rainwulf
Jan 22, 2004
I must post less.

Nerobro posted:

Before I go into this to far, I have never seen a motor cooled by imersion in a fluid. H2 cooling seems perfectly sane, as does air. As does running cooling fluids through the stator. I have heard of rotors having slip rings and cooling water too.



Believe it or not, some gasoline pumps in cars are cooled by the actual fuel flowing through them.

Awesome thread by the way, thinking of questions to ask.

Cheesemaster200
Feb 11, 2004

Guard of the Citadel

SeaBass posted:

It is not as common as it should be, but with OSHA being more assertive about assessing arc flash hazards, design engineers will be more diligent about protective device evaluation and coordination. Or they can pay me to do it for them :)

Honestly, for all of the reports I have reviewed, less than half are done correctly and that is because the systems are so small there is little room for error. The larger the system, the more room for something to get overlooked or not considered as a fault current contribution.

The problem is that you can't coordinate most molded case circuit breakers below around 100A, especially for arc flash. If you have low fault currents in your system you are going to have a lot of incident energy at your downstream breakers and coordination is next to impossible without using fuses.

quote:

I've often heard this could happen and have seen it in video, but had never seen it first-hand until one of the contractors I work with mis-wired a load bank- essentially feeding the full output of a 480V 400kVA transformer into a pair of 30' long #12 control wires. Damned things whipped like crazy! The 2A fuse blew almost instantly, but the magnetic forces from that much instantaneous current was amazing.
My favorite gently caress up was when a contractor we were working with connected an ABCN busway to a NCBA switchboard connection. Talk about a bolted fault. They energized the thing and almost knocked out the entire building. It was an old building so coordination was not the best Oops...

I also talked to a guy who apparently shorted some control wiring in a generator in a power plant, tripping the output breaker and turbine. This in turn tripped out the other generators (as the load was spread to them), which tripped out the plant, which tripped out all of Guatemala City, Guatemala. Don't know if it was for real, but I found it funny..

Cheesemaster200 fucked around with this message at 17:23 on Sep 29, 2011

Nerobro
Nov 4, 2005

Rider now with 100% more titanium!

rainwulf posted:

Believe it or not, some gasoline pumps in cars are cooled by the actual fuel flowing through them.

They are, they are also typically reciprocating pumps, so the same action that actually pumps the fuel is not wasted on "moving the armature" through the fluid. It's a clever set of design choices!

rainwulf
Jan 22, 2004
I must post less.
A question to ask of the Op, or relevant members, what are the typical specs of station batteries?

Size and whatnot? Like all things industrial, im assuming they are massively supersized versions of the battery in your car, but im just curious as to HOW supersized they are!

Drheat
Feb 20, 2008

Nerobro posted:

They are, they are also typically reciprocating pumps, so the same action that actually pumps the fuel is not wasted on "moving the armature" through the fluid. It's a clever set of design choices!

I have changed many fuel pumps on American and Japanese cars and have never seen a a reciprocating pump. they have all been standard brushed DC motors that drive a gear type positive displacement pump.

A few years ago the fuel pump on my Caravan died after 250,000 miles. I cut the pump apart expecting to find worn out brushes. I was shocked to find the brushes still at 50%, but the commutator had worn away to the point there was no more copper left, just the fiber insulating material.

Ossetepo
Mar 12, 2011

rainwulf posted:

A question to ask of the Op, or relevant members, what are the typical specs of station batteries?

Size and whatnot? Like all things industrial, im assuming they are massively supersized versions of the battery in your car, but im just curious as to HOW supersized they are!

By station batteries, do you mean backup DC power source batteries at a generating station or substation, or load leveling batteries? I can talk at some length about the first, but know fairly little about the latter.

rainwulf
Jan 22, 2004
I must post less.
The last fuel pump i pulled apart was the EFI pump for a honda, and it was a strange kind of turbine pump that used two wheels with small vanes on the outside.
It wasnt positive displacement, which was even weirder.

This is the closest i have come to finding the exact type of construction.

http://www.freepatentsonline.com/6799941.html

here is a better image and basically the same as the one i pulled apart.
http://www.tradekorea.com/product-detail/P00019222/Fuel_Pump.html

Anyway, back to electricity!!!

rainwulf fucked around with this message at 04:47 on Sep 30, 2011

rainwulf
Jan 22, 2004
I must post less.

Ossetepo posted:

By station batteries, do you mean backup DC power source batteries at a generating station or substation, or load leveling batteries? I can talk at some length about the first, but know fairly little about the latter.

any/both?
backup dc power source at a station, is that backup for the station itself? or backup for generation capacity? are there batteries even that big?

Ossetepo
Mar 12, 2011

rainwulf posted:

any/both?
backup dc power source at a station, is that backup for the station itself? or backup for generation capacity? are there batteries even that big?

Backup batteries at a generating station or substation are for providing DC power (or AC, via an inverter) to systems that need it in the event of a loss of their normal power source. For example, when the turbine-generator at a nuclear generating station is tripped, it can no longer provide power to the station. The normal 1st backup is the offsite power feed. If offsite power is lost, the 2nd backup(s) are the emergency diesel generators. If one or more EDGs are lost, DC battery banks are designed to provide power to those loads necessary for the safe shutdown of the reactor. I can post more later about the batteries we use for backup if you're interested - they're not really all that exciting, just large series arrays of midsized lead or Ni-Cad cells.

Load leveling, or grid storage, batteries are large battery arrays connected to the transmission grid and used to absorb transients in energy demand - if load drops off the grid, such as when an area is blacked out, that energy charges the batteries. If load suddenly increases, such as when large industrial equipment is placed in service, the batteries are depleted. Chemical batteries are not really the preferred way to do this - compared to other energy storage mechanisms, they're expensive and failure prone. I don't really know enough about the battery technology that is used to say much about it.

While it would be technically possible to locate a load leveling battery at a generating station, and thus provide backup for that stations generating capacity, that is not normally done. It's more economical and failure-resistant to use an off-site load leveling mechanism to support the grid while bringing online more generation capacity at other plants. The exception to that is for more intermittent generation methods, like solar or wind, some locations do have local energy storage to fill in when it gets cloudy or the wind dies, which gives the grid operators more time to bring the peakers online to hold up the grid.

shame on an IGA
Apr 8, 2005

On the topic of load leveling, is compressed air energy storage still a thing? We got a brief mention of it being researched while in high school but I've never heard if it panned out.

babyeatingpsychopath
Oct 28, 2000
Forum Veteran

I'm a commercial electrician. I love all the stuff that happens on the upstream side of the green boxes on the pads outside.

I am also curious about the coordination stuff; It seems to me like you CAN just put a 200kA fuse with 5k let-through in front of 5kA stuff and call it good, but I don't know for sure.

I got to tour a decent sized GE co-gen plant about a year ago. I can't remember their output in MVA, but it was a fairly large gas-turbine direct-coupled to a hydrogen-cooled genset with the exhaust feeding a steam turbine coupled to another hydrogen-cooled genset about 200 yards away. The switchgear room in there was neat.

I've also been to the building (but not inside) of the Artesia DC-DC link that connects the Eastern grid to the Western grid. Apparently the thyristor bank looks like a giant scientist's apparatus that feeds some plumbing nightmare. The DC bus is just a bunch of 18" copper rods going through the wall, and it looks like oversized plumbing pipe. I wish I could have gone inside.

Question time: do you guys still follow the NEC, or is there another standard? I know there are a bunch of sections for "over 600V, nominal" and whatnot, but they're so very short, comparatively.

Adbot
ADBOT LOVES YOU

Three-Phase
Aug 5, 2006

by zen death robot

rainwulf posted:

A question to ask of the Op, or relevant members, what are the typical specs of station batteries?

Size and whatnot? Like all things industrial, im assuming they are massively supersized versions of the battery in your car, but im just curious as to HOW supersized they are!

The ones I've seen are set up in arrays that provide about 120VDC for breaker control. They aren't really that large, I've seen them stored in a cabinet about the size of a photocopier.