You can: log in, read the tech support FAQ, or request your lost password. This dumb message (and those ads) will appear on every screen until you register! Get rid of this crap by registering your own SA Forums Account and joining roughly 150,000 Goons, for the one-time price of $9.95! We charge money because it costs us money per month for bills, and since we don't believe in showing ads to our users, we try to make the money back through forum registrations.
 
  • Post
  • Reply
internet celebrity
Jun 23, 2006

College Slice
Alright so. After a morning of flipping breakers and running back and forth I feel like I know more and less at the same time. The good news is that with the entire house shut off there's no current on the water pipe, so it's not something like a neighbor's broken neutral returning current through my good neutral through the water pipe (I don't 100% know what this means but I read that it happens sometimes).

I found a few breakers that individually cause the current in the water pipe to change. Basically every breaker that services something in the basement affected it, as well as one kitchen breaker and an unlabeled breaker that I haven't identified yet. Is this something that any regular electrician will know how to fix or am I way off in the land of weird edge cases with my electrified water?

I also hooked my guitar up to my laptop on battery power to find the breakers making the most noise. With everything off there's the expected amount of ambient noise so that's a bit of a relief, I'm not living in an electromagnetically cursed location where it's impossible to record stuff. But for the most part, any breaker that affected current in the water pipe made noise. The loudest breaker was the one the kitchen GFCI outlets are on. I got an outlet tester last week and it says they're all properly grounded so I'm not sure what to make of that, there's nothing plugged in to them. The breaker with the basement ceiling lights and outlets was pretty loud too. The lights were all switched off so it's not dimmers or fluorescent lights making the noise, it's just the breaker being switched on. And finally the furnace breaker was making a lot of noise for some reason. So knowing all this, what do. Again, is this regular electrician work or do I need some kind of EMI expert for this?

Adbot
ADBOT LOVES YOU

H110Hawk
Dec 28, 2006
Something, somewhere, is leaking current to ground. You can pay an electrician hourly to solve this. It's around $1000/day.

Next step is to unplug everything on a given breaker, but let's start easy. Do you have any 220v appliances with 3 prong outlets? Unplug those and see if it goes away.

internet celebrity
Jun 23, 2006

College Slice
My only appliance with a 3 prong 220 plug is my dryer and unplugging that and/or shutting off the breaker doesn't affect the reading or the noise whatsoever. Should I unplug all the appliances and everything on each circuit repeat what I just did? I feel like it may be related to the basement light/outlet wiring given what I've seen so far, that breaker causes the biggest change and makes the most EM noise. There are also a few (unused) ungrounded 2 prong outlets on that breaker.

H110Hawk
Dec 28, 2006

internet celebrity posted:

My only appliance with a 3 prong 220 plug is my dryer and unplugging that and/or shutting off the breaker doesn't affect the reading or the noise whatsoever. Should I unplug all the appliances and everything on each circuit repeat what I just did? I feel like it may be related to the basement light/outlet wiring given what I've seen so far, that breaker causes the biggest change and makes the most EM noise. There are also a few (unused) ungrounded 2 prong outlets on that breaker.

Yes, start with the biggest change and work from there. 2 prong outlets shouldn't be effecting it - they don't even have ground. 3-prong-220v can leak voltage L1-G to power the 120v control board is why I suggested it. Otherwise yeah, start testing.

Have a laptop with a video camera? Setup your meter on a zoom call. Join it from your phone. Unplug things and watch it go until it auto shuts off and you have to go turn the meter back on.

Shifty Pony
Dec 28, 2004

Up ta somethin'


Even if something is leaking current to a ground conductor, shouldn't that just be joining with the house neutral at the main panel/disconnect and going noiselessly up the service neutral?

I wonder if the ground/neutral bond is hosed up. Can you check and see if there is a potential between ground and neutral on the basement circuit (and other circuits).

Also you might want to check the water main coming in to make sure the previous owner didn't install some stupid magic "treatment" device that is applying current to the water.

babyeatingpsychopath
Oct 28, 2000
Forum Veteran


H110Hawk posted:

Have a laptop with a video camera? Setup your meter on a zoom call. Join it from your phone. Unplug things and watch it go until it auto shuts off and you have to go turn the meter back on.

This is brilliant.


Shifty Pony posted:

Also you might want to check the water main coming in to make sure the previous owner didn't install some stupid magic "treatment" device that is applying current to the water.

This is something so crazy I never would have thought of it.

KOTEX GOD OF BLOOD
Jul 7, 2012

Turns out Buna-N is food safe so I ordered those. I'll have to find out now whether I wanted medium or soft. Thanks for the link!

H110Hawk
Dec 28, 2006


:toot: They were finally able to get started on this today! Nothing is wired up yet, and they have 3 more batteries to install Monday pending some change they have to ask the fire department about. 2 of the battery modules were supposed to go on the block wall to the left but some last minute measurements realized a mistake in their initial ones. Now we're going up. They need to verify the vertical clearance required by the FD - Enphase (and UL) say these specific modules can do 6", standard plans/prior generations required 36" or something. I don't care how high they go, that's my neighbor's and the electricians servicing them's problem.

The hilarious wire coming out of the conduit in the ground there was a whoopsy doodle once they were done moving the main panel and couldn't figure out where the heck the pool pump was getting its power. It will be cleaned up / figured out by the time final inspection rolls around. Yes we have gotten 3 feet of rain so far this year and yes that is a NEMA 3R rated splice, why do you ask? What are you a narc?

devicenull
May 30, 2007

Grimey Drawer

H110Hawk posted:



:toot: They were finally able to get started on this today! Nothing is wired up yet, and they have 3 more batteries to install Monday pending some change they have to ask the fire department about. 2 of the battery modules were supposed to go on the block wall to the left but some last minute measurements realized a mistake in their initial ones. Now we're going up. They need to verify the vertical clearance required by the FD - Enphase (and UL) say these specific modules can do 6", standard plans/prior generations required 36" or something. I don't care how high they go, that's my neighbor's and the electricians servicing them's problem.

The hilarious wire coming out of the conduit in the ground there was a whoopsy doodle once they were done moving the main panel and couldn't figure out where the heck the pool pump was getting its power. It will be cleaned up / figured out by the time final inspection rolls around. Yes we have gotten 3 feet of rain so far this year and yes that is a NEMA 3R rated splice, why do you ask? What are you a narc?

That's really interesting you have a switch between the battery and system controller, and no rapid shutdown switch

My install has no switch between the battery and system controller, and a rapid shutdown switch outside. That battery disconnect isn't doing much, because if you've got the IQ8 inverters they'll continue to make power even w/o the battery.

Why are they doing a bunch of individual batteries? Enphase makes brackets/covers to wire 3 of them all in one unit.

H110Hawk
Dec 28, 2006

devicenull posted:

That's really interesting you have a switch between the battery and system controller, and no rapid shutdown switch

My install has no switch between the battery and system controller, and a rapid shutdown switch outside. That battery disconnect isn't doing much, because if you've got the IQ8 inverters they'll continue to make power even w/o the battery.

Why are they doing a bunch of individual batteries? Enphase makes brackets/covers to wire 3 of them all in one unit.

The plans have both, there's an AC disconnect box between the batteries and the controller. There is a RSD that is drawn but not yet installed that is coming off the controller. :shrug:

Can you post this bracket thing? Because "I don't know" is the answer.


H110Hawk fucked around with this message at 05:26 on Feb 25, 2024

Extant Artiodactyl
Sep 30, 2010
ah the 5p batteries...looks nice!
they don't get joined like the previous model, the 3 and 10t

i think it's a little unusual there's a disconnect between the controller and batteries when there's a breaker in there that will serve as a disconnect as well as a separate rapid shutdown switch but that's AHJ's for you

ROJO
Jan 14, 2006

Oven Wrangler

Extant Artiodactyl posted:

ah the 5p batteries...looks nice!
they don't get joined like the previous model, the 3 and 10t

i think it's a little unusual there's a disconnect between the controller and batteries when there's a breaker in there that will serve as a disconnect as well as a separate rapid shutdown switch but that's AHJ's for you

Yeah my city required disconnects between both my batteries and the solar combiner and the system controller, despite having basically redundant breakers and the rapid shutdown :shrug:

edit: also my controller is apparently super hosed and my whole system is in shutdown until enphase can come out with my installer on the 4th to fix/replace it

Hadlock
Nov 9, 2004

H110Hawk posted:

Is it all on the same circuit? You mentioned only having one outlet "on that side of the house/garage/something" - you only need one right where the circuit first starts from the panel assuming it's a home run from the panel to that outlet. Then you're good to go for the whole circuit. Or use a GFCI breaker.

I wouldn't bother putting your fish electrolysis machine on a GFCI yet though - it's just going to trip it. (I'm suggesting you throw it away or move it indoors first.)

Honestly I think given my playing with electrical habits being closely aligned with my posting habits (i.e. poorly thought through and frequently wrong) it's best I just do all GFCI breakers. They're not cheap but not that crazy expensive and I'm bound to do something wildly dangerous with our generator and/or welder

H110Hawk
Dec 28, 2006

Extant Artiodactyl posted:

ah the 5p batteries...looks nice!
they don't get joined like the previous model, the 3 and 10t

i think it's a little unusual there's a disconnect between the controller and batteries when there's a breaker in there that will serve as a disconnect as well as a separate rapid shutdown switch but that's AHJ's for you

ROJO posted:

Yeah my city required disconnects between both my batteries and the solar combiner and the system controller, despite having basically redundant breakers and the rapid shutdown :shrug:

Yeah it's odd but of all the BOM costs a lockable disconnect is so low on the list of stuff it didn't even dawn on me that it was weird until you pointed it out. I guess it's to guarantee to input voltage from the batteries while working on the controller? On a high level I understand wanting a visual indicator that 20kwh w/ 30kw output is isolated in case the internal controllers decide to start outputting despite an ordered shutdown.

ROJO posted:

edit: also my controller is apparently super hosed and my whole system is in shutdown until enphase can come out with my installer on the 4th to fix/replace it

:ohdear:

Extant Artiodactyl
Sep 30, 2010

ROJO posted:



edit: also my controller is apparently super hosed and my whole system is in shutdown until enphase can come out with my installer on the 4th to fix/replace it

hoping for a good outcome. when i did an install with an enphase tech/engineer for a unique setup, he had us set up a relay the wrong way and it ended up frying a transfer switch board
i also had one system controller be completely dead on arrival in a similar way, during commissioning it went into shutdown and never came out. thinking there's something up with whatever they're using for that low volt rapid shutdown initiation.

H110Hawk
Dec 28, 2006

Extant Artiodactyl posted:

hoping for a good outcome. when i did an install with an enphase tech/engineer for a unique setup, he had us set up a relay the wrong way and it ended up frying a transfer switch board
i also had one system controller be completely dead on arrival in a similar way, during commissioning it went into shutdown and never came out. thinking there's something up with whatever they're using for that low volt rapid shutdown initiation.

:ohdear: :ohdear: Guess I should have asked about a bypass mode.

Extant Artiodactyl
Sep 30, 2010

H110Hawk posted:

:ohdear: :ohdear: Guess I should have asked about a bypass mode.

the shutdown mode still lets line voltage through to the loads, it just renders the solar and batteries inoperable. theoretically i guess it could fail in a way that has it trying to power the loads from empty battery but i haven't seen it. there's a tiny switch underneath a "don't touch this without talking to support" sticker that i think toggles it between on and off grid mode without the installer app getting involved.

compared to generac, whose failure modes were more "you're up a creek", the enphase issues i've seen were usually limited to the initial install window and were more annoying than anything else. costly to the installer and not the customer

H110Hawk
Dec 28, 2006

Extant Artiodactyl posted:

the shutdown mode still lets line voltage through to the loads, it just renders the solar and batteries inoperable. theoretically i guess it could fail in a way that has it trying to power the loads from empty battery but i haven't seen it. there's a tiny switch underneath a "don't touch this without talking to support" sticker that i think toggles it between on and off grid mode without the installer app getting involved.

compared to generac, whose failure modes were more "you're up a creek", the enphase issues i've seen were usually limited to the initial install window and were more annoying than anything else. costly to the installer and not the customer

Yeah, my plan if this stuff decided to poo poo the bed was to immediately tear that sticker off and make sure any actual technician who showed up knew it was intact when they arrived. :v:

ROJO
Jan 14, 2006

Oven Wrangler

Extant Artiodactyl posted:

the shutdown mode still lets line voltage through to the loads, it just renders the solar and batteries inoperable. theoretically i guess it could fail in a way that has it trying to power the loads from empty battery but i haven't seen it. there's a tiny switch underneath a "don't touch this without talking to support" sticker that i think toggles it between on and off grid mode without the installer app getting involved.

compared to generac, whose failure modes were more "you're up a creek", the enphase issues i've seen were usually limited to the initial install window and were more annoying than anything else. costly to the installer and not the customer

Yeah I had to resort to the hidden switch to actually get normal power back into my house. For whatever reason, just shutting everything down with breakers but not manually throwing that switch only allows 1 of my 110 legs into the house. Hence the "super hosed" nature of my controller.

horse_ebookmarklet
Oct 6, 2003

can I play too?
Ok, how screwed am I here.

1970s home, metallic conduit with copper conductors. Conduit is ground.

I am replacing some switches with smart switches. Before I bought them, I confirmed my switch box has neutrals.
While I was in there, I noticed that the neutral was tied to ground in the box. I understand this to be bad and unsafe, as now the ground has a potential path to normally carry current.


So I replaced the switch, removed that illegal neutral-to-ground, and now the lights don't work. With my multimeter, I see a 120v potential between neutral and ground, 0v potential between neutral and hot.
I think whoever wired this used the conduit for NEUTRAL!
I went to a nearby outlet to try and pull a neutral from there, to discover that outlet no longer works, it is also tied back through the switchbox conduit. Of course there are wires going out of this problem outlet, off to someplace else to cause me problems.

I am going to get a licensed electrician in here, but closest appointment is Monday.
What do I do till then? Should I put the illegal neutral to ground connection back? I just don't know what else is now connected only to hot or the ramifications of this.

kastein
Aug 31, 2011

Moderator at http://www.ridgelineownersclub.com/forums/and soon to be mod of AI. MAKE AI GREAT AGAIN. Motronic for VP.
I would leave it off for now. In fact I would turn off the breaker for that whole circuit if possible. I think you're right on the money with the conduit as neutral theory and that's definitely not ok.

devicenull
May 30, 2007

Grimey Drawer
I needed a couple grounds for an ethernet surge protector and some antenna equipment... anything wrong with this?



I just did ring terminals to the outlet mounting screws (that right wire is green even though it doesnt look it)

kastein
Aug 31, 2011

Moderator at http://www.ridgelineownersclub.com/forums/and soon to be mod of AI. MAKE AI GREAT AGAIN. Motronic for VP.
Perfectly fine. No need to insulate or anything. There might technically be a reason it needs to be physically protected being under a certain gauge but I can't think of one, I think all the reasons I've seen for that are based on protecting ground electrode conductors in article 250.

Shifty Pony
Dec 28, 2004

Up ta somethin'


I bet that somewhere along the daisy chain of devices there's a missed neutral connection which the ground-neutral connection in that box was hiding. Leave the circuit off and make note of what else doesn't work. If you feel up to it open up those boxes looking for a neutral that isn't hooked up (or a janky connection), otherwise just having a good idea of what is on that circuit will help out the electrician.

horse_ebookmarklet
Oct 6, 2003

can I play too?

kastein posted:

I would leave it off for now. In fact I would turn off the breaker for that whole circuit if possible. I think you're right on the money with the conduit as neutral theory and that's definitely not ok.

I ended up leaving it off, this seemed wise.


Shifty Pony posted:

I bet that somewhere along the daisy chain of devices there's a missed neutral connection which the ground-neutral connection in that box was hiding. Leave the circuit off and make note of what else doesn't work. If you feel up to it open up those boxes looking for a neutral that isn't hooked up (or a janky connection), otherwise just having a good idea of what is on that circuit will help out the electrician.

Going to go digging into the boxes tomorrow. Not going to cancel the electrician till I find it though!
I definitely panicked when this first happened, but watching youtubes on "open neutral" I might be able to figure it out...
I have counted 4 switch boxes (totaling 10 switches), 5 light fixtures, 5 outlets, and one day/night photocell. A few of these being outdoors.
I have a feeling I will be in the attic very soon, knees throbbing as I scrabble across 16" on centers.

shame on an IGA
Apr 8, 2005

Shifty Pony posted:

I bet that somewhere along the daisy chain of devices there's a missed neutral connection which the ground-neutral connection in that box was hiding. Leave the circuit off and make note of what else doesn't work. If you feel up to it open up those boxes looking for a neutral that isn't hooked up (or a janky connection), otherwise just having a good idea of what is on that circuit will help out the electrician.

wouldn't this

quote:

With my multimeter, I see a 120v potential between neutral and ground, 0v potential between neutral and hot.

also imply that the open section of neutral wire is shorted to the hot leg somewhere?

also see some red wire in that box, my guess is a PO completely hosed up trying to install a three way switch somewhere

shame on an IGA fucked around with this message at 18:22 on Mar 2, 2024

Shifty Pony
Dec 28, 2004

Up ta somethin'


It could just mean something else upstream of that box was using that neutral/ground connection.

lovely drawing:



Neutral is purple because white doesn't show on white. Box with the now-removed ground/neutral is second from left, neutral isn't connected at the far right box. If that light bulb is "on" no current will flow but, the neutral will show 120V since there is a connection between hot and neutral via the light.

H110Hawk
Dec 28, 2006


City or FD said "no" to close spacing, or they got bored waiting. I do not care and had told them a week ago they could do this if they wanted. I cannot see this from any direction I use the house, there are mature plants blocking the view from the road.



So close. Final hookup + testing is monday or tuesday weather permitting, final permit inspections are all Thursday at which point I can submit my PTO. I need to find out what they did there with that WR GFCI outlet which is powering the pool pump. Ironically if they wound up wiring it into the controller to go "down" when the grid goes down that would be hilariously ideal.

Extant Artiodactyl
Sep 30, 2010
the poor bastards who had to raise those ~110lb units that high

kastein
Aug 31, 2011

Moderator at http://www.ridgelineownersclub.com/forums/and soon to be mod of AI. MAKE AI GREAT AGAIN. Motronic for VP.
I see a couple code violations (but not big ones)

Conduit must be strapped even if it is under the length (30in IIRC) allowed between a box and the first strap.

Box offsets would make it look nicer, but I totally understand not wanting to do them, I only learned to do them easily a few weeks ago myself. I used to get them wrong more than I got them right because I just trial and errored it instead of actually doing the math.

H110Hawk
Dec 28, 2006

kastein posted:

I see a couple code violations (but not big ones)

Conduit must be strapped even if it is under the length (30in IIRC) allowed between a box and the first strap.

Good thing you're no snitch. :toughguy:

Extant Artiodactyl posted:

the poor bastards who had to raise those ~110lb units that high

Yeah I said was happy to wait on the answer because I certainly wouldn't want to have to hump them up a ladder, or worse have to service them up there. They laughed and said they don't care they aren't super heavy. :shrug: I imagine the head guy had uh, paperwork to do that day and couldn't make the job site.

kastein
Aug 31, 2011

Moderator at http://www.ridgelineownersclub.com/forums/and soon to be mod of AI. MAKE AI GREAT AGAIN. Motronic for VP.

H110Hawk posted:

Good thing you're no snitch. :toughguy:

What? I didn't see poo poo

(I just thought you might want to see it and decide if you are going to have them fix it before inspection, some inspectors may let it slide or not even know, I see this violation all the time and have committed it myself)

H110Hawk
Dec 28, 2006

kastein posted:

What? I didn't see poo poo

(I just thought you might want to see it and decide if you are going to have them fix it before inspection, some inspectors may let it slide or not even know, I see this violation all the time and have committed it myself)

(I appreciate it, I'll bring it up in passing when I go by on Monday. Our new city inspector is more "by the book" on a lot of stuff since he's both good at his job and undoing a lot of previous inspector lack of fucks. Thankfully he's also reasonable, these electricians do a lot of work around the city and have precisely 0 advertising. Their website is a single picture titled "website.gif" which looks like someone's kid did it to make a 1-pager for print.)

KKKLIP ART
Sep 3, 2004

I am not sure if this is quite the right place to ask this question but since it deals with electricity and I don’t want to burn my place down, here it goes:
I have a cheap led light that is powered by 2 AAA batteries that I would like to instead see if I could power off of USB. Are there any legit battery replacement options?

Is something like this legit?

babyeatingpsychopath
Oct 28, 2000
Forum Veteran


KKKLIP ART posted:

I am not sure if this is quite the right place to ask this question but since it deals with electricity and I don’t want to burn my place down, here it goes:
I have a cheap led light that is powered by 2 AAA batteries that I would like to instead see if I could power off of USB. Are there any legit battery replacement options?

Is something like this legit?

Those are legit. I use USB-rechargeable AAA batteries, but if you want to put a cord in there, something like that works fine.

The Electronics Thread might also have some other options.

The easiest solution (and 100% not recommended, but I've done it before) is just cut the end off of a USB charge-only cable and attach red and black to + and - inside the case and be done with it.

Hungry Squirrel
Jun 30, 2008

You gonna eat that?
I just replaced my ceiling fan. It has a globe light fixture. I want to use a smart bulb but I can't find a smart bulb that is both rated for enclosed fixtures and the right size to fit through the opening in the globe, but not a candelabra shape/base. I have a replacement light kit that I got second-hand but the connectors are different.

This is the existing fixture:



This is the new light kit:



If there is a smart bulb, not much bigger than A19, that will work in an enclosed fixture, I'm happy. If I can get a new fixture that will have the same connector, that's good too, or if it's simple to re-wire (nothing much harder than stripping a wire and using a wire nut) I'm happy with that also. I don't want to burn the house down, but I also really don't want to have the electricians who hung all my lights come back again.

babyeatingpsychopath
Oct 28, 2000
Forum Veteran


Hungry Squirrel posted:

I just replaced my ceiling fan. It has a globe light fixture. I want to use a smart bulb but I can't find a smart bulb that is both rated for enclosed fixtures and the right size to fit through the opening in the globe, but not a candelabra shape/base. I have a replacement light kit that I got second-hand but the connectors are different.

This is the existing fixture:



Post the wiring of the existing fixture on the lighting side. You're going to be connecting the black and white wires of your new kit to exactly two of the wires you see there and putting wire nuts on the other two. Just can't tell which for certain from the current pictures.

Hungry Squirrel
Jun 30, 2008

You gonna eat that?
The existing kit looks like this:



I should also clarify that I'm looking for one of the fancy programmable color-change bulbs. The white ones that tick the boxes are readily available.

babyeatingpsychopath
Oct 28, 2000
Forum Veteran


Looks like the on/off switch with speed control for the fan is down there in the light unit. That's annoying.

Adbot
ADBOT LOVES YOU

shame on an IGA
Apr 8, 2005

Have you tested it with a Philips Hue bulb yet and can you borrow one from a friend to try it out if not? They're about the most compact RGB bulbs I've tried but too expensive to commit to before you know it'll work for sure