Combat Pretzel posted:Friend just asked me, whether Arduinos are generally reliable. What does this have to do with HVAC, you might ask. Well, the control board of his gas boiler apparently broke, so he wants to YOLO it on his own with an Arduino controlling the boiler unit (controlling gas valve, pumps, burner unit). And he's not exactly the coding and electronics guy to begin with. Like that's not going to go wrong, right? jesus gently caress please convince him not to do this. combustion controls are like only a hundo, and are based on decades of experience and reliability testing to be failsafe. Please tell him that if he fucks it up and blows up his house, the insurance people will laugh at him and hold him liable for any damages.
|
# ? Apr 10, 2021 23:30 |
|
|
# ? Jun 6, 2024 06:25 |
|
Combat Pretzel posted:Friend just asked me, whether Arduinos are generally reliable. No. Combat Pretzel posted:Well, the control board of his gas boiler apparently broke, so he wants to YOLO it on his own with an Arduino controlling the boiler unit (controlling gas valve, pumps, burner unit) Dear god no. Tell your friend to explain to you in great detail what a watchdog is and why it's essential on computerized industrial control systems and even if he somehow answers that correctly tell him to never use an arduino for anything that could kill someone if it goes wrong. corgski fucked around with this message at 23:44 on Apr 10, 2021 |
# ? Apr 10, 2021 23:42 |
|
stratdax posted:?? Not "whatever", I addressed the fact that the normal advice (which applies to most systems and climates) may not apply to a desert environment in the part you cut out. You are also assuming that he won't run the AC at all. I was trying to consider all possibilities in my suggestion, and you quote me to disagree as if I were wrong and you know everything about OP's situation.
|
# ? Apr 10, 2021 23:54 |
|
MRC48B posted:jesus gently caress please convince him not to do this.
|
# ? Apr 10, 2021 23:54 |
|
He wants to control a gas fired pressure vessel with an arduino? If he does this call the gas company on him. Edit: just read your last post to the end. Good job. Even if he can't get it working just narc on him regardless. Tell them he's trying. Edit edit: have him send you a picture of it because it sounds amazing. Post it here and to your gas company or fire station. H110Hawk fucked around with this message at 00:22 on Apr 11, 2021 |
# ? Apr 11, 2021 00:20 |
|
angryrobots posted:You are also assuming that he won't run the AC at all. stratdax posted:Any humidity formed from condensate leftover from when the AC was running will be unnoticeable. Again, ?? Why are you so pissy bud. Relax.
|
# ? Apr 11, 2021 01:24 |
|
stratdax posted:Again, ?? What is even happening here? You "won". Leave it at that.
|
# ? Apr 11, 2021 01:28 |
|
Settle down, stratdax.
|
# ? Apr 11, 2021 02:28 |
|
HVAC thread getting hot, obviously needs a coil clean, maybe a refrigerant charge. I had to be talked out of making a custom hydronic setup for my wood stove with an Arduino, that was probably a good thing.
|
# ? Apr 11, 2021 02:41 |
|
Elviscat posted:HVAC thread getting hot, obviously needs a coil clean, maybe a refrigerant charge. If you're just using it as a glorified IOT thermostat on the RGYWBO, knock yourself out. Don't use arduinos for anything life safety critical, like gas valves or really anything that has a lot of potential energy. They make purpose built controls for that, and they are better than anything you would come up with homebrewing.
|
# ? Apr 11, 2021 05:28 |
|
Yeah, you really want all the life safety interlock logic (for example over and under pressure sensors, refrigerant leak, CO, flame detect + gas valve, exhaust backspill, etc etc) to be hard wired logic designed by people who determined failure modes to be failsafe, used hardware components that are rated by the manufacturer for such use and have a known B10d or MTBF rating, etc etc etc. The MCU software should only be in charge of emissions+efficiency strategy/temp management/etc, so if it fucks off into the great beyond, the thing just stops working instead of blowing up the house or pumping it full of monoxide because it failed into a dangerous state. I would think long and hard before I would take on that project and I've designed life safety equipment for multiple industries already. Just loving buy another, they're cheap and you'll never get back the time you spent. It sounds like he's not smart enough to know he's not smart enough to do this. kastein fucked around with this message at 15:42 on Apr 12, 2021 |
# ? Apr 12, 2021 15:39 |
|
I work for a commercial/industrial burner manufacturer and I will definitely attest that rolling your own combustion control is profoundly stupid. Unless it's your job, but even then I relegate the baseline safety to a commercial control and then add on fancy PLC stuff for non-critical safety functions whenever I can.
|
# ? Apr 12, 2021 16:26 |
|
We've made a decision in remodelling our kitchen that I think is cascading into some unintended complications that I've never had to solve before. Wife wanted a 36 inch gas range for more space with 6 burners, but the ranges she likes are all around 48k to 63k BTUs total, which I believe needs 400 to 600cfm of ventilation on the range hood. I also thought that code (if not international, then definitely CA) now requires make-up air for ranges over 400CFM. Is there an easy way of doing this or is it probably going to be an expensive addition of additional fan(s) and ductwork? Edit: alternatively recalculate since she would not likely be running every burner at full at the same time? The two largest boilers only get me to 36k BTU's, but I think having to have her remember to s only use a combination of burners would be a no-go. PageMaster fucked around with this message at 05:48 on Apr 16, 2021 |
# ? Apr 16, 2021 05:44 |
|
MRC48B posted:If you're just using it as a glorified IOT thermostat on the RGYWBO, knock yourself out. Hell, even for that when I was contemplating DIYing a thermostat I was still designing it with relay-based interlocking so it couldn't physically call for hot and cold at the same time and a connection to an external mechanical thermostat that would disconnect the Arduino until manually reset if it was triggered to ensure the pipes couldn't freeze if it stopped working. Obviously not entirely necessary, but when my homebrew code on a cheap device would have the potential to cause thousands of dollars in damage if it went wrong while I wasn't home I wanted fail-safes. I ended up not doing it because my landlord was already sketchy about my Nest after the heater failed (four years later, and due to the flame tubes rusting out rather than anything a thermostat could cause) but still. wolrah fucked around with this message at 21:49 on Apr 16, 2021 |
# ? Apr 16, 2021 21:44 |
|
I'm buying the house I've been renting and living in for the past 6 years. We had a home inspection and the inspector pointed out that our boiler is 60 years old and we should probably think about a replacement sooner rather than later. I'm starting to learn more about boiler/radiator systems, but I'm wondering if there's anything I should keep in mind in regards to brands. At some point I'll talk to hvac companies and get some quotes and stuff, but it seems they each do only a couple of brands so I want to be sure I'm informed to be able to compare different options. Most of what I can find talking about comparing specific brands seems to appear almost ai generated content that I don't really get much info from. I'm also thinking of doing a ductless mini split system for AC, since we just have window units and since it's radiator heat there's no ducts for central air. So basically same observation about installers and brands, and same question about what brands are good or bad.
|
# ? Apr 17, 2021 02:04 |
|
FISHMANPET posted:I'm buying the house I've been renting and living in for the past 6 years. We had a home inspection and the inspector pointed out that our boiler is 60 years old and we should probably think about a replacement sooner rather than later. Gas fired? Oil? Is it cheaper energy wise to use the mini splits for heating as well? (depends on your cost of fuel vs electricity and your climate) Does your state or utility offer any incentives for home performance upgrades (such as a more efficient boiler or adding insulation)?
|
# ? Apr 17, 2021 17:07 |
|
Gas boiler, we're in Minnesota so I doubt that a mini split would be cost efficient or even capable of keeping up. There's also no insulation in the house so that's on the agenda as well, and I know it won't make much sense to do sizing for a brand new HVAC system on such a leaky house that we intend on sealing up.
|
# ? Apr 17, 2021 18:43 |
|
Phil Moscowitz posted:Thanks to everyone for the very helpful advice! Lots of research and discuss with our contractors. Just as a follow up, the second HVAC sub (our chosen sub, not the GC’s) came in and can absolutely run the ductwork as the architect had originally designed without any additional furr downs and keeping the downstairs system downstairs (avoiding the need for ducts running through the second floor). We will need a mini split in the addition but it’s the best option. We discussed high velocity systems with the architect who likes them and has used them, but none of the contractors had ever done one. We’re going to pay about 20% more but are also getting better equipment than the first sub was selling us (Amana v. Comfortmaker). Anyway thanks again for the advice!
|
# ? Apr 19, 2021 15:58 |
|
Don't worry about the name on the HVAC equipment. Comfortmaker is owned by Carrier, and Amana is owned by Daikan which bought Goodman. I don't know how much the product lines differ, but like a lot of things in the world, there is only 3 or 4 real OEM's out there with lots of different brands. Installation quality and dealer service is more important than the name brand of the equipment.
|
# ? Apr 19, 2021 16:36 |
|
Just reading reviews and looking at the noise/seer ratings, lifetime compressor warranty for Amana, really.
|
# ? Apr 19, 2021 17:57 |
|
A lifetime compressor warranty is a gimmick. It's the cheapest part of a compressor failure. Meaningful things like refrigerant, cleaning the lines, replacing the TXV, etc aren't covered.
|
# ? Apr 19, 2021 18:09 |
|
This industry has compressor manufacturing down to a science. DOA units are very rare. If your compressor died, something else in the system killed it, and it didn't happen overnight.
|
# ? Apr 19, 2021 19:07 |
|
If the compressor fails for any reason, they will replace the entire outdoor condenser unit. Maybe it’s not as good as it sounds but it seems better than the standard 5 year/10 year warranties?
|
# ? Apr 19, 2021 20:11 |
|
Phil Moscowitz posted:If the compressor fails for any reason, they will replace the entire outdoor condenser unit. Maybe it’s not as good as it sounds but it seems better than the standard 5 year/10 year warranties? It's better than nothing surely, just don't think it's not going to be a few grand to get it done.
|
# ? Apr 19, 2021 21:29 |
|
Phil Moscowitz posted:If the compressor fails for any reason, they will replace the entire outdoor condenser unit. Maybe it’s not as good as it sounds but it seems better than the standard 5 year/10 year warranties? It's better than a stick in the eye but I'm really not sure it matters. In all reality you'll need other work, they probably aren't covering even the labor to replace the outdoor unit (but at least it should come with SOME refrigerant in it) and by the time you're likely to see a compressor failure we'll probably be on to yet another refrigerant so whatever amount you need to make up will cost a ton of money to the point where you're more likely to swap the entire system. At least that's how things have been working for the last few decades. So I wouldn't pay much of a premium for a warranty like that.
|
# ? Apr 19, 2021 22:57 |
|
Lifetime compressor warranties are a total gimmick, the only reason a compressor is gonna die under 15 years is if you let a refrigerant leak go untreated for years or you're converting from r22 to r410a and you don't pull a proper vacuum/rx11 flush
|
# ? Apr 20, 2021 05:18 |
|
Ace of Baes posted:Lifetime compressor warranties are a total gimmick, the only reason a compressor is gonna die under 15 years is if you let a refrigerant leak go untreated for years or you're converting from r22 to r410a and you don't pull a proper vacuum/rx11 flush How hard/expensive/stupid is it to convert to r410a? I have an old r22 system that was very weirdly retrofitted into the house and nobody is willing to entertain replacing it and just wants to sell me mini splits instead. If the outdoor unit finally blows up I want to know if it's somehow possible to swap that with a new R410a unit. The more I know ahead of time the better, if this dies on me in peak summer my wife is going to write whatever check it takes to get AC back if I can't make it happen quickly.
|
# ? Apr 21, 2021 22:35 |
|
mcgreenvegtables posted:How hard/expensive/stupid is it to convert to r410a? I have an old r22 system that was very weirdly retrofitted into the house and nobody is willing to entertain replacing it and just wants to sell me mini splits instead. If the outdoor unit finally blows up I want to know if it's somehow possible to swap that with a new R410a unit. The more I know ahead of time the better, if this dies on me in peak summer my wife is going to write whatever check it takes to get AC back if I can't make it happen quickly. Have you considered calling a friend with an EPA license while the your wife is out to come vac out the R22 right now? "Oh no, it broke."
|
# ? Apr 21, 2021 23:11 |
|
mcgreenvegtables posted:How hard/expensive/stupid is it to convert to r410a? I have an old r22 system that was very weirdly retrofitted into the house and nobody is willing to entertain replacing it and just wants to sell me mini splits instead. If the outdoor unit finally blows up I want to know if it's somehow possible to swap that with a new R410a unit. The more I know ahead of time the better, if this dies on me in peak summer my wife is going to write whatever check it takes to get AC back if I can't make it happen quickly. Any competent contractor should be capable of this. Typically you must replace outdoor unit, flush old lineset, replace indoor coil/metering device, add a filter drier, leaktest, then evacuate, charge, and runtest. Is the indoor unit in some terribly inaccessible place?
|
# ? Apr 21, 2021 23:58 |
|
mcgreenvegtables posted:How hard/expensive/stupid is it to convert to r410a? I have an old r22 system that was very weirdly retrofitted into the house and nobody is willing to entertain replacing it and just wants to sell me mini splits instead. If the outdoor unit finally blows up I want to know if it's somehow possible to swap that with a new R410a unit. The more I know ahead of time the better, if this dies on me in peak summer my wife is going to write whatever check it takes to get AC back if I can't make it happen quickly. You need to find a better hvac company. You can pretty much always put a package unit on a roof, and you could just remove the air handler from the equation entirely. I don't recommend converting to r410a before replacing both your air handler and condenser, having matching brand and age condenser and air handler, or if you get a roof package unit, a single new unit with a self contained lineset (the refrigerant lines that run in a loop between the compressor and the two coils). R22 isn't that much more expensive than r410a yet and you shouldn't need refrigerant unless you have a leak, which is gonna cost you some cash and is probably a good time to replace your unit. Can you elaborate more on where your air handler is located? Is the house 2 story or 1 story? Do you have a pitched roof, do you have an attic access?
|
# ? Apr 22, 2021 05:00 |
|
I’m pretty sure it’s a rule that AC systems always break at the worst time. Last night I noticed our downstairs unit outside fan running but it didn’t sound like the compressor was running and it was a little warmer than set temp on the thermostat. Our bedroom wall is right next to the outdoor units so you can tell when things kick on/off. Great, I knew it was probably the capacitor since the fan was running but no compressor, but it’s like 11pm on a Saturday. The part is under warranty but I was probably looking at 400 for the labor and after hours/weekend service call to replace it. Long story short, got lucky and found an ace hardware about 30 minutes away that had a 40/5 440v on the shelf that was open on Sunday. 17 bucks and I’m back in action. I’m going to order a couple spares and keep them on the shelf since this Texas heat seems to kill these things. I’ve already replaced both systems capacitors once and the systems are less than 3 years old. I might as well order a set of spare contactors as well. Well that was my Sunday morning hope yours was better
|
# ? Apr 25, 2021 18:40 |
|
Jeezus, two replacement caps in three years? Are your outdoor units on the south side of the building or something?
|
# ? Apr 25, 2021 20:57 |
|
Yeah you might as well just replace them annually in the spring. Why risk it.
|
# ? Apr 25, 2021 21:16 |
|
Hed posted:Jeezus, two replacement caps in three years? Are your outdoor units on the south side of the building or something? Southwest side, full south Texas sun. H110Hawk posted:Yeah you might as well just replace them annually in the spring. Why risk it. Not a bad idea. Cheap insurance for sure. Filters and caps in the spring lol
|
# ? Apr 25, 2021 21:26 |
|
If this becomes a pattern consider uprating to a pair of capacitors, one 40mfd, the other 5mfd. if it's the heat killing them, this may give you more safety margin. manufacturers use dual caps for cost savings, not because they are actually better at anything.
|
# ? Apr 25, 2021 21:44 |
|
Just pick up a turbo cap, they come with a 5 year warranty.
|
# ? Apr 26, 2021 02:27 |
|
Ace of Baes posted:Just pick up a turbo cap, they come with a 5 year warranty. I saw those, are they worth the money? The 5 year warranty is nice, but it won't do anything when the cap eventually fails at the worst time possible (with my luck). My current plan is to just pick up a couple genteq caps for like 15 bucks each. If they last 2.5 years, that's 10 years of caps for the price of 1 turbo 200 (using amazon pricing). I'm fine just keeping a couple on the shelf of my garage. One unit uses a 35/5, the other a 40/5. 30 bucks to keep a set of spares on the shelf doesn't seem like a bad deal.
|
# ? Apr 26, 2021 18:54 |
|
skipdogg posted:I saw those, are they worth the money? The 5 year warranty is nice, but it won't do anything when the cap eventually fails at the worst time possible (with my luck). My current plan is to just pick up a couple genteq caps for like 15 bucks each. If they last 2.5 years, that's 10 years of caps for the price of 1 turbo 200 (using amazon pricing). I'm fine just keeping a couple on the shelf of my garage. One unit uses a 35/5, the other a 40/5. 30 bucks to keep a set of spares on the shelf doesn't seem like a bad deal. Spares are key.
|
# ? Apr 26, 2021 19:53 |
|
skipdogg posted:I saw those, are they worth the money? The 5 year warranty is nice, but it won't do anything when the cap eventually fails at the worst time possible (with my luck). My current plan is to just pick up a couple genteq caps for like 15 bucks each. If they last 2.5 years, that's 10 years of caps for the price of 1 turbo 200 (using amazon pricing). I'm fine just keeping a couple on the shelf of my garage. One unit uses a 35/5, the other a 40/5. 30 bucks to keep a set of spares on the shelf doesn't seem like a bad deal. Just buy a new one any time you consume your spare. I feel like past 2 spares you're really not buying yourself anything. Even beyond 1 spare you're way into diminishing returns.
|
# ? Apr 26, 2021 19:58 |
|
|
# ? Jun 6, 2024 06:25 |
|
skipdogg posted:I saw those, are they worth the money? The 5 year warranty is nice, but it won't do anything when the cap eventually fails at the worst time possible (with my luck). My current plan is to just pick up a couple genteq caps for like 15 bucks each. If they last 2.5 years, that's 10 years of caps for the price of 1 turbo 200 (using amazon pricing). I'm fine just keeping a couple on the shelf of my garage. One unit uses a 35/5, the other a 40/5. 30 bucks to keep a set of spares on the shelf doesn't seem like a bad deal. Turbos usually last a lot longer, you'll probably go past the warranty by at least a few years before you need to replace one Also if a turbo goes out before the warranty you know there's something wrong with your unit, and you should probably have a professional check it out. It's also not great to run your compressor/condenser fan motor/blower motor with a weak cap either, caps lose capicitance over time and a weak cap can cause a motor to over amp, especially if it's hot, which will cause damage to the motor windings. A lot of compressor with start assist kits will even run with completely dead run caps. Ace of Baes fucked around with this message at 04:41 on Apr 27, 2021 |
# ? Apr 27, 2021 04:02 |