angryrobots posted:If that's legal, it shouldn't be. Way too easy for the unknowing next owner of the house to remove the panel cover and bypass the interlock. Philosophically, better to have a safe legal way of cheaply hooking up a generator than driving idiots to suicide plugs in the dryer outlet, ya know? e: here's one Cutler Hammer sells: https://www.platt.com/CutSheets/Eaton/Generators-MechanicalInterlockCovers.pdf grover fucked around with this message at 20:21 on Aug 10, 2013 |
# ¿ Aug 10, 2013 20:15 |
|
|
# ¿ May 8, 2024 16:43 |
|
Three-Phase posted:Sure. grover fucked around with this message at 10:54 on Aug 17, 2013 |
# ¿ Aug 17, 2013 10:50 |
|
Rurutia posted:I have a bit of a weird rear end electrical issue. I have asked an electrician to come in and paid him $90 to open all the sockets and check the arc fault breaker itself then tell me he has no idea what's going on, so I'm hoping to get a bit of advice on either finding another electrician or some idea on what the problem is really. Smoke alarms are supposed to be on a breaker that's attached to lights so you can tell when it trips. They're also required to have battery back-up, and battery-powered smoke alarms will run for years on those batteries, so it's not THAT big a deal from a safety standpoint. If you don't have battery-back-up smoke alarms, you've got the wrong kind and should replace them. grover fucked around with this message at 14:35 on Aug 30, 2013 |
# ¿ Aug 30, 2013 14:27 |
|
Rurutia posted:Uh, is $90/hr considered cheap? It's mid to high around here I thought. Do you have any suggestions on how to find a good electrician? This guy came recommended online, and my extensive searching for electrician reviews have come up pretty scarce for recommended ones. AFCIs are sensitive to ground faults, and can trip on neutral-ground faults (which allow some neutral current to flow through the neutral) as well as actual arc faults. Excessive leakage current through failing bathroom fans and such can cause issues, too, but AFCIs are not generally as sensitive as GFCIs to this. As can wiring gently caress-ups like combining neutrals from different circuits. You may have an arc fault in a wall. Like if a nail is driven through a cable and shorts it out some of the time. This seems to be very rare compared to electricians simply loving up and handling neutrals wrong, though.
|
# ¿ Aug 30, 2013 16:19 |
|
Guy Axlerod posted:What's the point of hard-wired smoke alarms if you still have to replace the battery every year? Or did I misunderstand, and it's a single, central battery? And no, you don't really have to replace the batteries every year, that's just an extremely conservative recommendation. They make infuriating and too-physically-painful-to-ignore beeps when they die. Which is usually like 5+ years later. At which point, I think you're supposed to actually replace the whole smoke alarm. e: 10 year replacement schedule, apparently.
|
# ¿ Aug 30, 2013 22:49 |
|
kastein posted:... I'll have to report back after I test out their interaction with the ATS and generator, however. I hear that often causes nuisance trips so I'm curious to see how it goes, seeing as I've been careful about my N/G bonding I don't think it will be a problem but I could be wrong.
|
# ¿ Aug 31, 2013 01:53 |
|
ncumbered_by_idgits posted:Nuisance tripping from turning off high-current loads, particularly from removing the plug from the receptacle under load. Vacuums, circular saws, etc.
|
# ¿ Aug 31, 2013 04:25 |
|
Raised by Hamsters posted:My limited understanding of wiring is curious - what even happens in that situation? Someone letting grounded metal brush up against neutral terminals? Shouldn't that be pretty easy to avoid?
|
# ¿ Aug 31, 2013 15:37 |
|
ncumbered_by_idgits posted:How so? grover fucked around with this message at 16:19 on Aug 31, 2013 |
# ¿ Aug 31, 2013 16:14 |
|
ncumbered_by_idgits posted:That'd be a GFCI. grover fucked around with this message at 18:08 on Aug 31, 2013 |
# ¿ Aug 31, 2013 18:05 |
|
Guy Axlerod posted:I guess what I don't understand is why someone would pay extra for a hard-wired system when they still have to replace the batteries?
|
# ¿ Sep 2, 2013 14:17 |
|
kastein posted:I thought CAFCI was combined series and parallel AFCI, not combined AFCI and GFCI, but I haven't been too clear on it. Most AFCI breakers (new and old) have integrated ground fault detection as part of the fault detection circuitry, though do NOT qualify as GFCI because tolerance is set higher- 30ma vice 5ma for GFCI.
|
# ¿ Sep 3, 2013 01:48 |
|
stupid puma posted:I've got a couple of questions. I don't know much about electrical so please bear with me. The easiest safe/legal way to retrofit is to install GFCIs. You don't need a GFCI per receptacle; one GFCI can protect the entire string. Find where the first one in the string is, and install a GFCI there. grover fucked around with this message at 22:54 on Sep 3, 2013 |
# ¿ Sep 3, 2013 22:31 |
|
IRC R313 covers smoke alarms in houses. It requires smoke alarms to be powered from building power with battery back-up. It's silent on whether it needs a dedicated circuit or can share, which means either way is fine, but they all have to be interconnected so that if one goes off, they all go off. One advantage of sharing a lighting circuit is that you'd know if the breaker tripped and be able to address it. Since you have battery backup, losing power for short periods of time isn't all that big a deal. grover fucked around with this message at 15:57 on Sep 4, 2013 |
# ¿ Sep 4, 2013 15:55 |
|
ToxicFrog posted:Is it just me, or does that look kind of charred? If so, what do I do? Can I safely strip off the charred section and connect it to the other half of the breaker, or will I have to replace the entire breaker? Also, is this a sign that it just wasn't connected to the breaker properly, or that the wire is not rated for the amount of current through it, and I'll need to either rewire that entire circuit (please god no) or replace the breaker with one with a lower current limit? And if I'm completely wrong and it's meant to look like that, can I safely assume it was a transient increase in power draw from the dehumidifier that tripped it and hook everything back up again? Turn power off to the whole panel and give that wire a tug- if it comes out, that was for sure your problem. I would torque down every other bolt in the panel at the same time. A loose neutral or ground is likely the cause of the 40V readings- readings like that are often phantom voltages due to poor connections. Probably the ground in this cases as you'd likely have experienced issues if the neutral was loose. Check all the ground connections in all the boxes in that circuit if you can. grover fucked around with this message at 20:35 on Sep 14, 2013 |
# ¿ Sep 14, 2013 20:21 |
|
Bobulus posted:Googled around and am getting different answers in different places. Grounding issue: I'd take this to your landlord though and get him to bring an electrician in to take a look at it. It's a serious safety issue no matter which way it ends up. grover fucked around with this message at 20:36 on Sep 14, 2013 |
# ¿ Sep 14, 2013 20:30 |
|
Bobulus posted:You check this with the breaker off, right? I just tried that and could get no continuity between the two. This is not a "you broke your dishwasher" kind of thing; this is a pre-existing building code violation the landlord should be responsible for fixing. It's the type of thing that can leave the unit uninhabitable until repaired. Possible caveat: are these outlets GFCI protected? That's the only way they would be legal if ungrounded. If this is the case, the first breaker in each string should be a GFCI, and pushing the test button on it should kill everything downstream. If this is the case, they're supposed to be clearly labeled both GFCI PROTECTED and UNGROUNDED. If someone simply replaced the old 2-prong with 3-pring to avoid using adapters without doing anything else, it's illegal as gently caress. The hazard is that if an appliance shorts out, case will remain energized but it won't trip the breaker, and can lead to shocks and possibly electrocution.
|
# ¿ Sep 14, 2013 21:39 |
|
Bobulus posted:The only gfci outlets (IE, those with test buttons) I can find are in the kitchen, which is on a different circuit than the bedrooms I'm testing this in. I was assuming that the 3-prong ungrounded stuff was just grandfathered in at some point, it being a very old house, (especially since the remodeled room appears to have been done correctly), but if it is indeed impossible for them have done this legally, it gives me a lot more ammunition to get them to fix it.
|
# ¿ Sep 14, 2013 22:17 |
|
Slugworth posted:
Protip: add an "l" before the ".jpg" to get a smaller version of a giant imgur image. grover fucked around with this message at 23:30 on Sep 19, 2013 |
# ¿ Sep 19, 2013 23:27 |
|
Yep, sorry. On the bright side, your neighborhood is now far less likely to suffer blackouts when all your neighbors get EV cars.kastein posted:I've never seen a generator installed on a pole in a residential neighborhood before, nevermind 3 seperate ones for each hot leg. grover fucked around with this message at 00:23 on Sep 20, 2013 |
# ¿ Sep 19, 2013 23:34 |
|
This is from IRC2003 (condensed from NEC), but I don't think it's changed since then:
|
# ¿ Oct 7, 2013 23:32 |
|
Thermal protection switch. It'll cut the power if the can gets too hot.
|
# ¿ Oct 14, 2013 01:44 |
|
Skier posted:What is the recommended NEC 2011 code book? http://www.amazon.com/National-Elec...c+2011+handbook ? If you're just a normal homeowner and not an electrician, I'd actually recommend getting International Residential Code (IRC) instead of NEC. It includes all the applicable portions of NEC as well as all the rest of the building codes that apply to 1-2 family homes. It lags behind NEC by a cycle (IRC 2012 includes NEC 2011), so you'll still want to be aware of differences. grover fucked around with this message at 14:09 on Nov 5, 2013 |
# ¿ Nov 5, 2013 13:41 |
|
Guy Axlerod posted:In my mind, a real volt meter will have two important features: kastein posted:Agreed, I only use mine to check if the box is live still, and even then I double check with a voltmeter and/or table lamp after. grover fucked around with this message at 17:51 on Nov 10, 2013 |
# ¿ Nov 10, 2013 17:46 |
|
Entangled posted:I don't know if this is the best place for it, but as this thread has a good makeup of practicing electricians and DIY homeowners, I think it would appeal to both groups. Yeah, that site is a scam.
|
# ¿ Dec 1, 2013 05:43 |
|
Motronic posted:It's not safe or legal to do it for house wiring.....as in wall cable. That should be wire nutted or similar and in a box. As far as dealing with what's little more than an extension cord......there is no "code" to fall back on. The only people who would have any say about that is your insurance company.
|
# ¿ Dec 8, 2013 21:58 |
|
FCKGW posted:I have an upright freezer in my garage on a GFCI plug that seems to be tripping lately. When it trips it turns off all my outdoor outlets including the christmas lights. That said, garages are actually a terrible place for a freezer, though; they're not designed to work with the wild temperature swings. some texas redneck posted:What's an acceptable voltage drop on a fully loaded circuit?
|
# ¿ Dec 11, 2013 11:57 |
|
Loose lugs are some of the worst causes of weird poo poo happening. And so easy to prevent just by doing a final re-torquing of everything in the panel before energizing it like should be done anyhow.
grover fucked around with this message at 01:43 on Dec 22, 2013 |
# ¿ Dec 21, 2013 18:58 |
|
Is it a CFL? Sounds like it's simply dying. If the replacement works fine, that's a good indication the first bulb is destined for the garbage can.WeaselWeaz posted:Question about LED dimmers and old wiring. I'm looking to use LED bulbs in my basement and the lights are connected to a 2-wire switch. I want to put in a LED-compatible dimmer instead. Some reviews I've seen reference a ground connection being required, and I don't see the site and I'm pretty sure the box isn't grounded. I haven't bought a dimmer yet, but is this going to be a problem? grover fucked around with this message at 15:05 on Dec 22, 2013 |
# ¿ Dec 22, 2013 15:02 |
|
Motronic posted:Like the outlet the fireplace is plugged into? grover fucked around with this message at 19:45 on Dec 23, 2013 |
# ¿ Dec 23, 2013 17:00 |
|
Looks like both switches are wired up with switch loops. The big question is where they're going to. If you can find the other boxes in the circuit and how they're wired up, we may be able to make more sense of why it's not working right.
grover fucked around with this message at 00:21 on Dec 27, 2013 |
# ¿ Dec 27, 2013 00:18 |
|
Miyamotos RGB NES posted:I am not sure where the outlet is wired to (the one with the white and red wire coming out of it, and a black wire going nowhere) but I am 90% sure the switch controls the floodlights. Even though it is motion sensored, I am guessing this is so you can have them as "always on" if you have a backyard gathering at night and don't want to wave your hands around like an idiot every 30 seconds so your friends can have light. Might be worth your while to open up the box the light is in and see how it's wired up. As well as any other outlets you think may be controlling lights in your garage.
|
# ¿ Dec 27, 2013 00:45 |
|
A flying piece of posted:I picked up three heated rabbit water bottles. They say 'Don't use with an extension cord', like every electrical thing used for heating seems to. Unless I'm missing something, the worry is that extension cords will heat up, melt, and cause a fire due to the amps being drawn. Each of these bottles pulls 120 volts and 20 watts, which is less than .2 amps if I'm reading this correctly. Is it ridiculous to worry about plugging each of these into one three outlet, 14 gauge outdoor cord or am I going to burn my house down?
|
# ¿ Jan 25, 2014 20:13 |
|
Cosmik Debris posted:The home's breaker for that circuit would have probably tripped (hopefully) before anything serious happened.
|
# ¿ Jan 26, 2014 00:13 |
|
tater_salad posted:Since power had been out for a week or so in the area. (Wet heavy snow in october with leaves still on trees caused widespread outages usually with multiple lines down in a neighborhood.) The power company went door to door telling people that they were working on restoring power and that they should not try and kill the nice linemen who were restoring power. Can you tell when Katrina hit, solely by looking at this graph? Buy a loving CO detector and chain your generator up outside, it's not difficult and could save your life! grover fucked around with this message at 15:02 on Jan 26, 2014 |
# ¿ Jan 26, 2014 14:58 |
|
me your dad posted:We have a bare-bulb ceiling light with a pull-cord. When we turn on the light, it flickers and sometimes turns off. Lightly tugging at the pull-cord (not enough to engage the mechanism) fixes it after a few jiggles. I have checked the bulb and it is seated tightly in the fixture. What room is this in? An exposed pull-cord fixture is only legal in a veeeery narrow niche of applications, and illegal in virtually every application I see it used in. Landlord's electrician might need to fix it right while he's there, and put in an enclosed light and switch to operate it.
|
# ¿ Jan 29, 2014 15:24 |
|
Crotch Fruit posted:With all the lights on, flipping any switch will make them flicker. I have only 6 months left on my lease (maybe less if the rear end in a top hat below me keeps making noise complains and leaving threatening letters while I am at work. . .) and I told the manager on duty about this, she looked extremely un-interested but promised to send maintenance by someday. At least I have renters insurance for when this place catches on fire. The funny thing is I don't know how old this place, but it is one probably the newest apartment I have lived in yet. Bonus: Last night I discovered whenever I flip the dead bolt on the front door all of the lights dim.
|
# ¿ Jan 29, 2014 17:30 |
|
you ate my cat posted:I feel like this is kind of a dumb question, but - how do I measure current with a clamp meter on a 220 line? I get it on 110, you clamp around the hot and there you go. On 220, though, I have 2 hots and a ground. I'm just getting a 0 when I try to measure it. Do I have to measure the hots separately? If it's reading 0Amps on both lines, that either means there's too little current for it to measure, you're not using it right, or it's broken. Most likely broken- open it up and see if there's a blown replaceable fuse. grover fucked around with this message at 04:12 on Feb 16, 2014 |
# ¿ Feb 16, 2014 04:10 |
|
|
# ¿ May 8, 2024 16:43 |
|
SolidElectronics posted:Just measure one of the hots, same as you'd do on a 120V circuit. Assuming there's no neutral line and no ground fault, the same amount of current is flowing through both wires. If you put the clamp around both they'll cancel each other out which would explain your zero reading.
|
# ¿ Feb 16, 2014 04:46 |